Wiring Unlimited - Systems with multiple inverters

In the Wiring unlimited page 36, connections "A" is OK and "C" can not be used.

Can you clarify if Connection "B" is right or wrong?

It has cross and check at the same time. What does it mean?

1683734118785.png

wiring diagram
1683734118785.png (96.0 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Michelle Konzack avatar image
Michelle Konzack answered ·

It mean, the NEGATIV pole of the Battery SHOULD NOT be switched and every PLUS pole to the Inverters must have there own contact in the switch.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Mike Dorsett avatar image
Mike Dorsett answered ·

The reason for doing this (not switching the negatives) is that with 2 pole switches, you cannot guarantee that both poles will close simultaneously. If the positive makes first, then the communications cable, which is connected to the inverter negative, will carry the charging current for the inverter capacitors. This results in sufficient energy to destroy the communications interface, as it is non isolated. In countries where the installation standard REQUIRES boht poles to be switched, you either have to apply for an exception from the regulator, OR you can BOND the negative poles of all the inverters together - an equipotential bond. The negative power for the coms (GX) device should also be connected to this bond, as should the battery earth, if you are earthing the battery.

2 |3000