question

daza avatar image
daza asked

Server Rack for Pylontech batteries

Hi I’m looking at getting a server rack for Pylontec batteries I’m looking to get 2 US5000 batteries with possible space for two more as an expansion option. I have no idea what size server cabinet that I need.

I think I’ve seen something about it being 600mm wide by 600mm deep cabinet but I have no idea what the height is supposed to be for 4 US5000, any help around this is much appreciated.

storage
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

123-racks avatar image 123-racks commented ·
Good evening. We just had a call from a customer referencing this post, and he is ordering the same rack for his US5000 batteries as Gaza posted in December. I run 123 Racks and have researched this last year and even have thermostatically controlled heating / venting options for those needing it. Happy for you to search us online and look for yourself and reach out. This is not a sales post! Was just interested to get a call from this customer and he sent me a link to this post :-) Nice! And it's also a personal interest of mine. Just holding out for prices to fall even more ;-)


Useful to note, 1U is 1.75 inches. So a US5000 measuring 6.34 inches high would need 3.62U. And as 'U's come in whole numbers, that's 4U. Whether you want to leave space in-between each battery depends on your environment and your installer's advice. All the best!

0 Likes 0 ·
26 Answers
Duivert NL avatar image
Duivert NL answered ·

hello

i have 3 US5000 in one 16he rack, the US5000 is 4he and i left a space of 1he open between each US5000 and the top and bottom

if you are going to fill it with 4 US5000, then you would need 21he with the same spacing, you should not stack them directly!

also take care that you support the units from the rear, the racks ears are designed to hold them in place not to carry the weight!

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

daza avatar image
daza answered ·

@duivert thank you are you able to tell me what this is in U size as that’s what they seem to be termed over here. Are you saying the front is supported already I just need to support the back end of the battery so that the front hasn’t got all the weight?

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Juha Tuomala avatar image Juha Tuomala commented ·
I think those are supposed to be supported by shelves or L-edges that are attached to front and back posts and support the case from bottom corner all the way to back.
0 Likes 0 ·
Duivert NL avatar image
Duivert NL answered ·

1HE is 1U its the same!

there heavy (40kg each) so yes support the back

I made some brackets on the lef and right sides in my rack where the battery get supported

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

daza avatar image
daza answered ·

Anyone know to get a good U21 server cabinet in the UK? One with mesh front and back as I’m not sure how much these batteries will heat up.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

solar-sam avatar image
solar-sam answered ·

I'm exactly in the same position as you Dazza, have 2 US5000 batteries but thinking of doubling capacity. Seen one cabinet but its a hefty £750, which seems excessive. think we need U19 or U21 min for 4 batteries. They don't seem to give off much heat even when working hard. In fact my worry is the opposite as kept in unheated outbuilding currently, and hearing they don't like low temps, hence thinking of housing together in a cabinet. Dont mind doing some DIY support work to a right sized cabinet as they will need to take 160kg of batteries.

Appreciate anyones ideas??

Option then to import cheap rate during winter months plus decent storage amount in the summer.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

jonofe avatar image
jonofe answered ·

I'm using an 18U open rack from Startech (280£, up to 544kg) with Digitus rails (28£ each, up to 100kg each).

Fits for 4xUS5000 (19,6 kWh) or 2xUS5000 + 3xUS3000C (20,1 kWh).

Costs: slightly below 400£

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Craig Chamberlain avatar image
Craig Chamberlain answered ·

I bought a Samson SRK16 16U rack from Juno Records (juno.co.uk) for £115.22. It can handle 200Kg of total load or 150Kg if you use the included casters. I've currently got 3 x US5000 batteries installed as well as a network switch and patch panel but I could have fitted a fourth battery if I wanted to. The space between modules is about 20mm and I have supported the back of each module with a rack mount support kit from network-cabs.co.uk ( product code ADRMSB-150 £14.34ea ). I also got a cable management bar from the same company to support the battery and data cables (product ref ADCLBS-50 £6.60 ea )

HTH

img-8342.jpeg


img-8342.jpeg (4.1 MiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

k-k avatar image
k-k answered ·

You might look here: https://www.thomann.de/de/flyht_pro_alle_racks.html

"HE" means (DE: HöhenEinheit) or Unitheight.

Or go to your local music/guitar/pa-shop and ask for 19" flight-cases.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

daza avatar image
daza answered ·

@solar sam I used the pylontech brackets in the end they are stackable I’m gonna get a 4th US5000 at some point so I can comfortably not use peak cost units form my energy company, I have constructed a box warmer with PIR insulation board and a reptile bulb with fan to warm the box when the temp drops to 20 degrees so battery temp ranges from 20 - 34 degrees. Minimal energy used to keep it warm I would prefer not to have used it as it’s not ascetically pleasing but need to keep it warm due to an external garage from the house but it does the job.


img-4222.jpeg
img-4034.jpeg
img-4223.jpeg


img-4222.jpeg (3.2 MiB)
img-4034.jpeg (2.3 MiB)
img-4223.jpeg (3.0 MiB)
4 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Craig Chamberlain avatar image Craig Chamberlain commented ·
I was originally going to install my gear in my garage, mainly due to noise concerns, but ended up installing in my house after conducting a trial and deciding the noise was not so bad. But I was planning to build a similarly insulated box at least until I finished insulating the garage itself. The only suggestion I would make is to try to have two methods of preventing overheating, just to provide redundancy. Could just be two thermostat circuits in series, or could be an extractor which triggers at a higher temp, or even an overheat alarm.

The other thing to note is that the US5000 can only be stacked 3 units high with the Pylontech brackets according to the manual. That’s why I opted for the Samson server rack. That and the fact the Pylontech brackets were so expensive compared to the cost of my rack.

Good to see your setup come together.

0 Likes 0 ·
daza avatar image daza Craig Chamberlain commented ·

Cheers mate think they are very reserved on the stacking I’m gonna do 4 in a stack brackets are well built but I’ll deal with the consequences of a broken bracket then I’ll look at a rack which was my option before as the build would look so good but people wanted silly money for them.


The cover is only for the winter the top and all four sides just lift up to ventilation all around apart from the bottom.


possibly might get another Shelly to do a thermal alarm but it’s wired to thermal sensor to the GX so I can see battery and box temp on the VRM

0 Likes 0 ·
Craig Chamberlain avatar image Craig Chamberlain daza commented ·

I think you're probably right about Pylontech being cautious and I've not personally seen the brackets in person so can't judge how strong they are. But just bear in mind that the bottom module in a stack of 4 will have something like 120Kg of weight on the top of it and 160Kg of weight on the bottom so take care not to cause any crushing of the module enclosure.

Also, when you come to register your batteries with Pylontech in order to get the extended warranty, they ask for a photo of your installation so probably best not to send them a photo of a stack of 4 modules. ;)

Personally I'm finding that three US5000 modules is plenty to power my household all day, especially now that I've switched to Intelligent Octopus Go with at least 6 hours of off-peak electricity at 7.5p/kWh and potentially some additional adhoc charging slots at other times. Those extra 2 hours of off-peak grid really do make a surprising difference and are probably equivalent to another quarter of a US5000 battery module. What really simplifies things is the fact that I now get 15p/kWh for export at all times so my strategy is simply to fill the battery every night to 100% without needing to leave any space for predicted solar PV energy. Then if I am lucky enough to get decent solar production, I can just export it without worrying about conversion efficiency losses etc. I also don’t need to think about dumping home battery energy into our EV because that is never going to be better than just charging from the grid at 7.5p. The only wrinkle I need to resolve is to ensure that the adhoc charging slots don’t cause inadvertent discharge of my home battery into the EV but I have some ideas to solve that using Home Assistant.

My advice would be to hold off adding a fourth battery until you have the data to be sure that it’s worth the cost.

1 Like 1 ·
daza avatar image daza Craig Chamberlain commented ·
Ive not had any adhoc charging from Octopus I’m feeling cheated lol, when I got the 15p first thing I did was turn off the solar charge on the EV charger lol, yeah my house hold uses a lot looking at 15kW a day in peak hours and want run an electric heater while the missis is working from home, what I haven’t worked out how to do is tell Victron ignore solar to charge the battery and just dump the solar in the grid. My EV charger is outside of victrons view so I can just leave it plugged in without it draining the battery.


Yes will more than likely take a pic of the stack and register the four one but I may get a rack and stack them in there I spent a lot of time on wiring and ascetics just peed I had to hide it all so I’ll keep a look out but think I want a glass door so I can heat the inside still and still look at my handiwork lol

0 Likes 0 ·
daza avatar image
daza answered ·

@Craig Chamberlain so after hard thought and wanting to make the install nice I’m going to be pulling the trigger on a 20U Data cabinet later and will move all the garage network equipment in that as well as it’s going to be 300mm higher than the pylontechs rack it should have enough room for that and supports upto 800kg so should be good for 4 US5000 I’ll just move the heat light into the rack and hope there is enough space for everything lol

2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Craig Chamberlain avatar image Craig Chamberlain commented ·
Yeah I think you're doing the right thing and I'm sure you can resell your Pylontech brackets easily enough on eBay or something.

One tip I'll suggest although I'm sure you already know. If you anticipate adding a 4th battery module then install your existing modues towards the bottom of the rack so that you can easily add the new one, which will probably have later firmware, at the top to become the new master module. You need to have the module with the newest firmware as master and that means having it at the top or the little link port cables will be a bit too short.

I also wouldn't be surprised if such a thing exists as a server rack heater module that you could maybe install at the bottom of the rack, below the first battery so you can take advantage of convection.

Last thoughts are to be careful of condensation as that's the last thing you need around lithium batteries and electricity in general. I'm currently insulating my garage and it's incredible how much condensation occurs where you have cold steel cladding exposed to the air inside. I'm gradually adding 150mm of mineral wool to the walls plus a vapour barrier to prevent the moist air hitting the cladding. Hopefully by heating from the inside your rack will stay dry though.

1 Like 1 ·
Show more comments
solar-sam avatar image
solar-sam answered ·

some great tips here many thanks...Tried looking up Juno records, for that rack and could not find the Samson SRK16 one.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Craig Chamberlain avatar image Craig Chamberlain commented ·

Looks like it's out of stock at present unfortunately but here is the page:

https://www.juno.co.uk/products/samson-srk16-16-space-universal-studio-equipment/586846-01/

0 Likes 0 ·
solar-sam avatar image
solar-sam answered ·

Thanks have saved it as favourites for when its back in stock, solid sides as well. Just need to fit a front and rear and that's some protection straight away.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Craig Chamberlain avatar image Craig Chamberlain commented ·
Might be worth emailing their sales department so they can either let you know when they expect stock, or they might just say they don't expect to get them back in again.


The one I got was the last in stock at the time and arrived in a pretty beat up box and the rack had some very minor cosmetic damage. They were very good about it and offered a full return + refund or a 15% discount. I took the discount because I was able to assemble the rack so that the damage was at the back and hardly visible. I think I ended up paying just £98 for it total after the discount.

Yes it doesn't have a front panel but for my purposes I didn't care about that as it's in an under stairs cupboard and fits perfectly under one of the treads so can be pushed back out of harm's way. I've also got the cable tidy bars on the front to attach and route the cables so it forms a rudimentary bumper to protect the DIP switches etc.

0 Likes 0 ·
daza avatar image
daza answered ·

I finally pulled the trigger and ordered https://www.broadbandbuyer.com/products/30243-lms-data-cab-fe-20u-66na/specifications/#content

a lot more that @Craig Chamberlain but I got tired of waiting for a good secondhand one with the size I wanted and that wouldn’t cost the earth settled on this one still no idea if it’s good or not as I’ve not got it yet

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Craig Chamberlain avatar image Craig Chamberlain commented ·
That looks like a pretty nice rack @daza and although it cost a bit more than mine, I'd say it's a step up as a product with the front door etc. And let's face it, it's a relatively small cost compared to the cost of our projects as a whole! :)
1 Like 1 ·
solar-sam avatar image
solar-sam answered ·

that looks great Daza, did you have to order shelves as extras or does it come with some. Seems almost the same as some I've seen for £750

3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

daza avatar image daza commented ·

Cheers but not seen it in the flesh yet, Yes ordered 5 shelves and a power surge plug for the sever rack so I could put my network switch in there to, also ordered extra screws but the shelves come with screws so not needed, all in about 4 odd.

Even the eBay ones where coming in hot for second hand that I would have to hire a van to pick them up.

1 Like 1 ·
Craig Chamberlain avatar image Craig Chamberlain daza commented ·
Don’t sweat the cost @daza , you’re protecting your investment in the much more expensive battery modules. I’m hoping my batteries will last for 10-15 years and they cost around £4500 so to spend £100-£400 to protect them is just good business.
2 Likes 2 ·
daza avatar image daza Craig Chamberlain commented ·

so true @Craig Chamberlain ive just got my flood sensor to go in the rack trying to think at which level to put it I.
Either top or middle of the pack so I can make sure there is no condensation happening, just got to hope that the cables reach the batteries as only point seems from the middle base of the rack.

Ive got big some big glands that I can core out and put some of my damp poof paint on and then fit the glands which should make it long enough to get to the top battery, yeah I’m hoping for those years too.

0 Likes 0 ·
solar-sam avatar image
solar-sam answered ·

Been reading how our batteries certainly dont like temperatures below freezing and must stay above. Mine are in an unheated workshop, although double brick and insulated its only got a couple of freezers to add heat so not much. measured temps of cases and only 1 degree above room temp which is in itself almost ambient. Took a short term tip from another forum and put a decent cylinder jacket around them to help slow down and temp plunges and preserve any self heat generated. will remove in sping.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

solar-sam avatar image
solar-sam answered ·

ohh and the inverter which also gives off some heat.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

daza avatar image
daza answered ·

Mine hasn‘t Gone to zero, and that’s a single brick building, although I have the insulated box which works a treat but looks ugly the garage has only dropped to 9 degrees, The box is at a toasty 20 odd degrees, the positive cable is 12 degrees and the Negative cable is always the same temp as the garage and the batteries internal temp is 26/27 degrees on charge it’s 30 degrees I monitor everything.

Outside temp is 7 degrees my server is kicking out 17 degrees only thing that I’m not measuring it the temp of the Victron which I would like to do as I’ve now got a shelly flood sensor with temp sensor built in so I want that in the rack. And I’ll be putting the infrared bulb in the rack too, yes I’m going to loss a lot of heat and have the bulb working almost 24/7 in the winter on a 60watt bulb may buy another bulb so I have a straight swap when it blows.

I may see if I can use the thermostat that I have wired in the Victron to measure the victrons temp. So I should have the temp controlled that the batteries should never reach 5 degrees with all of the measurements but looks like they will be a lot higher than that.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

daza avatar image
daza answered ·

img-4418.jpeg@solar sam @Craig Chamberlain I’ve finally got the rack and installed the shelve, great thing is on wheels and has elephant feet so you can level out and put firmly in place. Batteries in tomorrow once I’ve wired the quatro loan unit up.


img-4419.jpegimg-4417.jpeg




img-4419.jpeg (2.7 MiB)
img-4417.jpeg (2.5 MiB)
img-4418.jpeg (2.4 MiB)
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Craig Chamberlain avatar image Craig Chamberlain commented ·
Looks great!
0 Likes 0 ·
daza avatar image
daza answered ·

@Craig Chamberlain I’m after a bit of advice, took longer to wire the cabinet than expected which leads me to my question finding it hard heating the rack with the 60watt infrared. it doesn’t appear to be transferring any heat but it looks like it is keeping the temp consistent. I’ve just ordered a 150w infrared bulb, but what do you think should I just get a server rack heater?

img-4420.jpeg


img-4420.jpeg (332.9 KiB)
6 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Craig Chamberlain avatar image Craig Chamberlain commented ·
I think I would rather rely on convected heat in this situation rather than radiated heat so I would tend to go for a thermostatically controlled rack heater. But you might need to blank off some of the vent slots to avoid all that heat just escaping into your garage. :)
1 Like 1 ·
daza avatar image daza Craig Chamberlain commented ·
Cheers mate now I’ve just got to find some where to put the unit, what size wattage wise I’m thinking 100watts maybe?

yeah I’m going to blank the lower ones, now just to find a small good one with temp cutoff.

0 Likes 0 ·
Craig Chamberlain avatar image Craig Chamberlain daza commented ·
It's hard to predict how much heating power you will need but as long as it can self-regulate safely then better to have some headroom if you can.


That all said, it seems a shame to have to waste precious energy, especially in the winter when you need it most, just to heat your batteries. Is there no way you can harness some of the heat from your multiplus, perhaps something like a mini cooker hood a safe distance away from the top of the multiplus so that it doesn't impede the airflow. I think 100mm is probably enough but check the manual. Then you could just have a duct fan and a length of ducting to bring that waste heat down to the batteries. You might still need the thermostatic heater for times when the multiplus isn't producing enough heat but even when it's running at 600w or so, it still gives off some warmth. Ideally try to find insulated ducting or wrap it with lagging.

Just an idea :)

0 Likes 0 ·
daza avatar image daza Craig Chamberlain commented ·
Cheers mate just ordered the heater and thermostat, it is 100watts, yeah I would love to have that energy but needs must to keep the batteries happy.


I’m so done with the install now just want it done now, just had to pack up my multiplus for repair which is annoying. nah one of the reasons I moved the the box from the batteries was for aesthetics.
0 Likes 0 ·
Craig Chamberlain avatar image Craig Chamberlain daza commented ·
What happened to the Multiplus? I'll have a search for a thread on that in the forum shortly. Sorry to hear you've had issues.

100 watts will hopefully be fine, especially if you block some vents and maybe even attach some of that silver foil bubble wrap to the inside of the rack body. Or even better, a multifoil insulation product.

I would seriously consider capturing multiplus waste heat as well though. :)

0 Likes 0 ·
daza avatar image daza Craig Chamberlain commented ·
Yeah I may get some of that foil bubble wrap, I’ve only just put out something on the forum re the multi, heater should be coming today which is good as it seems to be getting colder
0 Likes 0 ·
Arjen Geluk avatar image
Arjen Geluk answered ·

img-8352.jpeg

img-8353.jpeg

Just used a L-profile as a 19” substitute. Connects all front-panels inline and keeps them in place. Added rubber plates under all feet to reduce slack in the pylontech frames and prevent sliding. Very happy with all this.

,

image.jpgimage.jpgImage Caption

Just used a L-profile as a 19” substitute to connect all us5000 frontpanels inline. And added rubber tiles under each foot to prevent slack and an occasional slipping and sliding.


img-8352.jpeg (2.2 MiB)
img-8353.jpeg (2.2 MiB)
image.jpg (2.2 MiB)
image.jpg (3.4 MiB)
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Craig Chamberlain avatar image Craig Chamberlain commented ·
Looks great! I was in two minds about getting a rack which had a door and one that didn't and I'm glad I kept mine open because I like to see the Pylontech front panels. They are not ugly batteries in my opinion and it's useful to be able to see the LEDs.

Nice one.

0 Likes 0 ·
daza avatar image
daza answered ·

@Arjen Geluk nice you managed to use the pylontech brackets looks good @Craig Chamberlain nope I like the look of the Pylotech batteries too lol, so heater delivered and wired up now had to get heat resistant wire for it, thanks for the idea of the thermal blanket I’ve blocked some of the vent and just put a mat over the top vents so summer I can just take it off to ventilate here is the stuff that I got. Temp started to rise the Shelly reckons the rack is 21.8 but batteries still at 14 degrees they take ages to heat up. Thermostat set to 26 degrees so hopping they at least get to 20 degrees. Will know more in a couple of hours I guess.


img-4429.jpeg

img-4431.jpeg

img-4433.jpeg

img-4434.jpeg


img-4429.jpeg (3.5 MiB)
img-4431.jpeg (3.1 MiB)
img-4433.jpeg (2.5 MiB)
img-4434.jpeg (2.2 MiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

lee-taylor avatar image
lee-taylor answered ·

A really useful thread. I have had my four pylontech 5000's sitting on the floor in pairs which has been bugging me ever since I installed them. Seeing the photos above I have ordered the same cabinet. As far as temperatures go I use a repurposed Mac mini to run home assistant and this allows me to monitor the ambient and battery temps. My garage is internal with no heating and generally the battery temps seem fine. Its 7c outside currently and the batteries are at 12c. I am not planning on adding any additional heating but will monitor it just in case. I do have a couple of esp32 devices in home assistant in the garage. One measures the output from the inverter which is currently 23C. The other takes data from the mppt 450/100 out of the ve. direct connection.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

daza avatar image
daza answered ·

@Lee Taylor glad it helped and i wouldn’t rule out that heater mate that cabinet is very well ventilated ive now got ears for my switch so that lives in there now. the batteries with all the vents blocked as the door by the glass has gaps at the top and bottom all of that and the 100watt heater mine are sitting at 20 degrees it takes an age to heat the cabinet its only luke warm inside so rather gentle heat shelly reckons the temp is higher i may have to set them to battery temp. If you go for a heater get heat resistive wire but it’s hard as hell to strip.


img-4437.png

img-4438.png



img-4437.png (4.3 MiB)
img-4438.png (244.0 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

daza avatar image
daza answered ·

If you do nee any help heater wise contact https://uk.farnell.com/webapp/wcs/stores/servlet/TopCategoriesDisplayView?catalogId=10001&langId=44&storeId=10151 they have some technical know how as well the tech helped me select to items

2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

solar-sam avatar image solar-sam commented ·
Hi Dazza, Ive got the same cabinet as yourself now. Just a question I have, If you blocked up all the vents do you think you could get away with a smaller heater. Mine is in a outbuilding that is double wall but unheated, so doesn't really go below 5 degrees inside.

Now you have had some experience with yours might be able to judge if say a 20w would have done the trick.

0 Likes 0 ·
daza avatar image daza solar-sam commented ·

@solar sam sorry mate short answer no it wouldn’t even touch the sides! What I’ve done now is block the vents at the lower and high parts at the top and back the only one that I have left is the one at the top in the middle but I have a cover over it that I will uncover in summer to allow more ventilation I’m still toying with the idea of putting my AC fan on there and seeing if I can use the Shelly to output at a temp range wish I bought the cold and hot thermostat now lol as that could have done it. I’ve also lined the removable panels using double sided foam tape and the the silver foiled bubble wrap insulation. Also the gap of the glass stops the temp from building up it’s 6 degrees outside according to victron and the battery temp is 24degrees I think from memory I was managing 20degrees at minus temps. Where my heater is I used cement board to block that part of the slot where the cables enter I’m going to look for some big flexi conduit at some point so I can have all the cables protected and block the entry hole further. Hope this helps

img-4642.jpeg

img-4643.jpeg

img-4645.jpeg

0 Likes 0 ·
img-4642.jpeg (4.4 MiB)
img-4643.jpeg (2.6 MiB)
img-4645.jpeg (3.3 MiB)
solar-sam avatar image
solar-sam answered ·

Some great advice for the server rack and heating. Really appreciate all help. Believe we are on the cusp of a huge price crash in batteries and solar products much more than we've seen in the past. We normally see the price crash at the manufacturers and it slowly filters through despite some clear attempts to hold up prices and hence profiteering in the interim.

Just checked on Alibarba and the Pylontec US 5000 currently going for £576.76

see link below if it will display. Almost tempted to market them at current margins and help the green revolution that we really need.

Think import vat would be applied but may be worth investigation into the transport costs. If price is right I would love a very large storage capacity, gives huge flexibility on off peak charging and usage.

https://www.aliexpress.com/item/1005006188139055.html?spm=a2g0o.productlist.main.5.2dc77780FJ3ofk&algo_pvid=52ed41f9-ec1c-45a4-834c-a1e68cb841f4&algo_exp_id=52ed41f9-ec1c-45a4-834c-a1e68cb841f4-2&pdp_npi=4%40dis%21GBP%21960.60%21576.36%21%21%216000.00%21%21%40210387a117036810601642388e18c2%2112000036192373893%21sea%21UK%210%21AB&curPageLogUid=Y1MjSz2xrGSk

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

daza avatar image daza commented ·
lol I’m hearing about a crash I don’t see one though as I imagine they are going to just line their pockets with profit. I need a fourth one so a good price drop is very welcome my end lol
0 Likes 0 ·
solar-sam avatar image
solar-sam answered ·

looks good Dazza, glad I asked the question building on your experience. have ordered up some insulating materials already and will go down some lines.