max battery charge current with mppt and inverter

Hi all,

I have a small setup with a victron smart shunt 500A (and temp sensor) with victron smartsolar mppt 100/30, 24V battery bank (2x FLA C20 100Ah) and 2x 340W panels connected in parallel.

Currenty I have a non victron victron inverter. My max charge current is set at 20A. I was thinking of getting a few more panels to connect to another 100/30 mppt and altogether in a VE network all tied to rasp3B+.

As the power that I will produce will be quite a bit, so my question is if I get a victron 24V 1200VA inverter, are the MPPTs smart enough to see from the victron inverter the amps drawn and push more current to the battery/inverter above the max charge current. So, a hypothetical example, the solar panels can produce say 25A each (two MPPTs), the battery gets charged with 20A and 30A go to the inverter or will the MPPTs altogether just limit the current going to the battery/inverter at 20A regardless of the inverter load?

Logically in my mind, the VE network should be able to see the victron inverter load and adjust accordingly and push more than the max charge battery current. Maybe it is my wishful thinking.

Many thanks indeed for any help with this.

battery chargingMPPT SmartSolarinverter current draw
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
nickdb avatar image
nickdb answered ·

Smart networking isn't meant to be used in conjunction with a GX/venus device. Attach all the devices via VE BUS/VE direct to the GX/Pi and use DVCC to coordinate charging.

All well documented in the GX manual under the DVCC section.

5 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

saskak avatar image saskak commented ·
Many thanks for the reply. They all are connected in a bluetooth smart network and a VE direct cable (MPPT & shunt) to the Pi for logging purposes. I will read on the DVCC to see if the system can push current above the max charge settings to account for the inverter load.
0 Likes 0 ·
Show more comments
bigbadbob76 avatar image
bigbadbob76 answered ·

Yes, using DVCC you can limit the total charge current into the battery while also supplying the inverter/loads. just make sure you set the mppt to its maximum current.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

saskak avatar image saskak commented ·
Ahh, yes, thanks for that. Just read the DVCC section and the system will take the minimum charge current from the DVCC settings and the MPPT settings. Thus setting MPPT at max will be optimal.
0 Likes 0 ·

Related Resources

Additional resources still need to be added for this topic

VictronConnect VE.Bus charging manual