Hi All, does anybody know if there is a Victron preferred method of monitoring the grid connection in an ESS where the size of the supply exceeds the capabilities of the ET340 (65A per phase) and the standard Victron 100A CT? I think this system will be connected to a 250A three phase supply (still having the supply confirmed)

Can I just connect another Carlo Gavazzi meter like EM271 and expect it to work out of the box?

Energy Meter
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
janieronen avatar image
janieronen answered ·

From the manual: https://www.victronenergy.com/upload/documents/Energy_Meter_ET112/113406-Energy_Meters-pdf-en.pdf

" Q7: I want to use Current Transformers (CTs), is that possible?

Yes. You can buy a CG EM24DINAV53DISX, a CG EM530DINAV53XS1X or the CG EM530DINAV53XS1PFC directly from Carlo Gavazzi or one of their distributors. Even though Victron does not stock that type of meter, we do support it in our software. "


Look selection guide from Carlo Gavazzi for choosing correct clamp to suit your grid connection.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

hominidae avatar image hominidae commented ·

+1

EM530 accepts CT with 5A Output and up to 10kA on primary side.

Have a look here, as an example: https://www.gavazziautomation.com/nsc/HQ/EN/group/WC000002V39?WFCURTRAF2_C2000005=C2000005V2