Configuring Multiplus for off grid priority

So I got the multiplus hooked up for test. The AC side is not "installed", just a standard plug into a household socket and a single 3 pin test socket. Asides one or two tests of the inverter with the known limitations of no earth reference when in "Invertor Only" or if there is a grid fault, it won't be in "use" until the spark comes to do the AC side and install a ground rod. I also tested the charger.

So I have the inverter/charger itself working fine. I have the a RPI with Venus on it as GX device connected with a MK3 USB to the Multiplus. I

I also figured out the VRM remote config proceedure so have super user access to the Multiplus.

I also got MQTT working, although I would rather it connected to my broker and not make a local one.

What I want to look at next is configuring (or controlling) the Multiplus such that the grid is used as a "last resort", but otherwise continue to provide a "protected" circuit.


I would like:

Normal operation: Invert from battery to supply AC loads.

If AC loads exceeds the inverter capacity, add grid power.

If the DC voltage falls too low, feed AC loads with pass through. Ideally enable the charger at that point (optional) to support the DC loads also.

I can do this manually right now, but that isn't ideal.

I have considered DIY digital control mechanisms, maybe via MQTT, such that I can monitor the system and send controls to it when thresholds are reached.

I thought I'd ask, as the ESS eco-system in Victron exists, but I'm finding researching it a bit difficult. Obviously the vast majority of multiplus users consider the AC-In to be shore power.

Another option, I stumbled on, but not sure about, is to tell the Multiplus that AC-In is in fact a generator and should only be started when the DC is low. Is this a thing? Is it worth going that way?

Links to specific guides on ESS and "Favour solar, favour DC, AC-In only if strictly needed." would be helpful.


Cheers!


MultiPlus Quattro Inverter Charger
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

5 Answers
paul-campbell avatar image
paul-campbell answered ·

Hmm. It seems as though with the recent firmware it is steering me towards using the "Virtual Switch" instead.

The simple "Dedicated AC Ignore" options results in this:

1682438688654.png

There is a more complicated AC Ignore with a lot more options.

I think I will perform some experiments with the above this evening and see how it gets on. If I need to go to the more advanced config option I may have questions :)


1682438688654.png (73.4 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

paul-campbell avatar image
paul-campbell answered ·

I am reading this: https://www.victronenergy.com/media/pg/Energy_Storage_System/en/configuration.html

However, it's trying to cover too many scenarios at once. I'd need to mind map that in a diagram to digest it.

Items I don't like the look of. "Grid code password required". Grrr. The DNO have thus far replied with absolute silence. I figure they aren't interested in what I'm doing. It might prove difficult to get that, through official channels anyway.

ESS seems to be focusing on Victron gear integrations. Understandable. However it looks as though it bases battery levels on it's SoC. SoC is the most useless figure on any battery management system, always has been. You need expensive gear like VE smart shunts to get it even ball park right.

The other concern I have is surrounding the topology of the inverter and if it can do as I wish at all. As I understand it the Multiplus inverter uses a generated sine wave into a transformer. If AC-In is present this sinewave will be phase locked with the AC-In and it's amplitude increased to match it. Resulting in net 0 current.

Should an AC load come on inverter AC-Out side it will pull the transformer voltage down, but as it's now locked on the low impedence grid connection current will immediately flow from grid to the AC load. In addition, if enabled, the charger will allow current to flow backwards through the DC/AC converter and thus charge the batteries at the same time as supplying the AC loads.

Now. In my scenario I want it to produce power from the batteries to the AC loads. The only way it can achieve that, if I understand the topology correctly, is by increasing the amplitude of the inverted AC ABOVE that of the grid, so that net current flows 'from' the batteries. However, that also puts back pressure on the grid, which can lead to "export".

How does the multiplus handle this scenario? Does it uncouple the AC-In / AC-Out if the inverter is favoured over AC-In? How else can it push current in only one direction?

The blunt option is to put a smart switch on the inverter AC input and take control away from it. However, if I understand correctly I am far, far safer with the grid connected and the inverter in phase-sync with it and also coupled to the grid PNE.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

JohnC avatar image
JohnC answered ·

Hi @Paul Campbell

If you don't want to export, and even hope to be 'offgrid' much of the time, then don't use ESS. You have other Assistants onboard your Multi that can control ACIN on your terms. Take a look at the Generator Start/stop Assistant (in the Multi), but use the IgnoreAC function to switch ACIN rather than start a genset.

No grid code, 'smart switch', or fiddling needed. Ask if you need help with it, but it's far simpler than ESS.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

paul-campbell avatar image
paul-campbell answered ·

Thank you. Gives me a lead. I'll go down that path.

Got good news. The "tamed spark" says he will install the ground rod and help me install and make safe the AC side with RCD etc. Gonna cost me a days labour at hourly rate and parts/expenses, but at least he got the gist of what I needed and is happy he can make it safe. Including putting the panels up on the garage roof (instead of ground mounted in the garden) and earth them up.


2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

paul-campbell avatar image
paul-campbell answered ·

Tested the above with "contrived" values, like 100W load and 26.6V for battery which where easy to achieve conditions. Works under both conditions fine.

The only thing is the charger gets enabled with the AC input, which I haven't decided if that's always what I want. The other more complicated Ignore AC Input Virtual switch I think might cover that scenario as it includes charger enable/disable thresholds I believe.

Happy enough. Thanks for pointing me in that direction :)