BYD and Quattro never go to float?

Hi


Have set up VEConfigure on a Quattro and byd


As per settings

Battery type lithium

Charge curve fixed

Absorbtion voltage 55.2

Float voltage 55v

Absorbtion time 1 hr


When charging the battery’s the inverter goes in to absorbtion but it hasn’t charged over to float?


Is there something I am missing or is these normal and should just rely on the byd bms?


Regards

Mike







BYD
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
mvader (Victron Energy) avatar image
mvader (Victron Energy) answered ·

Hi Mike, yes normal.


When controlled by a BMS such as BYD has, it just shows Bulk & Float. Nothing else: Bulk whenever it’s on max current (ie. CC mode). And shows absorption when limited by voltage (ie. CV mode).


Best, Matthijs

12 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

mikeb avatar image mikeb commented ·

Thanks for the reply


Sorry for the next question but just wanted to make sure things are how they should be

My understanding was if DVCC was in use on the colour control solar would be prioritised if there was a genny running and didn’t need to be as the battery’s were fully charged and the solar was enough to cover loads


Will this still work the the byd system?


Regards

Mike

0 Likes 0 ·
mvader (Victron Energy) avatar image mvader (Victron Energy) ♦♦ mikeb commented ·

Hi Mike, indeed it does.

Note that normally prioritizing isn’t too necessary for such setup; better configure the generator to stop once there is enough solar. Matthijs

0 Likes 0 ·
mikeb avatar image mikeb mvader (Victron Energy) ♦♦ commented ·

Hi thanks for the reply


Can I just ask if you have some guide lines for generator stop/start soc voltage etc for the byd set up? Will be using the byd bms for the stop start on the colour gx


Is there another way your suggesting ? Ie the Quattro relay pair? And a assistant?



Regards

Mike

0 Likes 0 ·
mvader (Victron Energy) avatar image mvader (Victron Energy) ♦♦ mikeb commented ·

Hi Mike, best is to use the Color Control for start stop. It offers most flexibility.


Use the SOC condition. stop generator when full (100%); and stop when charge current very low, for example.


Make it start at the threshold as you wish. 10 or 20%. Or more of you want to keep a reserve.


Then, and this is important, add starting on voltage. This is to make sure the generator starts, even when SOC has drifted off. Voltage is a direct measurement: more reliable.


Set it slightly above advised dynamic cutoff values is what I would do.


And now, optionally, add a periodic test run.

Hope that helps


Matthijs




0 Likes 0 ·
Show more comments
victron-answers avatar image
victron-answers answered ·

That is normal.

When charging the BYD the target voltage is key, rather than the characteristic of the charging profile like in lead acid.

If the system is reaching and staying at 55V, all is well and should indicate a fully charged battery.