VE. Bus Error 18

Hello, we have Quatro 48/15000 3 master and 6 slave units, BYD LVL 15.6 kWh 12 batteries, Fronius Symo Eco 27 kW, Symo 20 kW, Symo 10 kw and MPPT 150/85 6 units.

The system has been operating as an off-grid. In the last month, it first gives Error 5 error, then Error 18 code. The system does not work.

We did cable checks, but it worked one day and gave the same fault again. I'm asking for a solution on this.

@Guy Stewart (Victron Community Manager)

error
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
Daniël Boekel (Victron Energy Staff) avatar image
Daniël Boekel (Victron Energy Staff) answered ·

Hi @veliozbek

This probably means that there are PV inverters that do not:

-reduce power when frequency shifts to control them, this leads to overvoltage on AC output and the Quattro's shut down due to overvoltage.


Check the settings of your PV inverters.

3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

veliozbek avatar image veliozbek commented ·
hello first of all thanks your help. Please you can explain detail how can reduce power
0 Likes 0 ·
Alexandra avatar image Alexandra ♦ veliozbek commented ·

@veliozbek

What programming was done on the Fronius inverters other than setting the Micro Grid?

What assistant did you program onto the inverters to control the frequency?

Is the BYD vharge voltages set to the on grid or off grid voltages on the victron and in the BMU?

0 Likes 0 ·
Show more comments
Alexandra avatar image
Alexandra answered ·

@veliozbek

Both of those errors relate to AC wiring issues.... check for loose connections.....

Check for shorts, wires mixed up like line and neutral or a ground issue....

Not sure how anyone on the forum will be able to help with that.

Error 5.

Error 18.


1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

veliozbek avatar image veliozbek commented ·

cevap için teşekkürler alexandar. Kabloları ve hatları kontrol ettik. Önce 5 hata veriyor bir kaç denemeden sonra 18 hata veriyor. Bugün yine uzaktan reset attım ara ara kontrol ediyorum. Şimdilik sorun değil, ama önereceğini tekrar kontrol edeceğini. Bir fprm'de BYD max şarj gerilimini düşürün ve fronius frekans kaymasını daha yüksek bir değere çekin diyor.

@Guy Stewart (Victron Community Manager)

0 Likes 0 ·
levistoth avatar image
levistoth answered ·

Hello Everyone,


I have the same issue with a system with the following configuration :


9 x Victron 15 kVA

3 x Fronius 25 kW on the AC output

80 x Pylontech us2000C


in ESS configuration, everything is working fine if the batteries SOC is low and we have where to use the produced energy, but soon as batteries get around 80% SOC we have this issue.


We have al the settings , what victron recomend both on the victron and both on the fronius (MC50, Control via Modbus)


What can we do, to not have this issue anymore ?


Thanks

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.