3 Phase Installation 3 x Quattro-II 48/5000 Generator Dimensioning

Hi all.

My installation: 3 x Quattro-II 48/5000 connected to 3 Phase Installation

  1. Is it possible to install a generator (230 V 1 Phase) at one of the 3 Quattros? Is the load balanced over the 3 Phases automatically?
  2. If Point 1 is possible, can i additionally install a second generator (230 V 1 Phase) at one of the other Quattros?

Thanks in advance for your answers.
Marc

MultiPlus Quattro Inverter ChargerGenerator3 phase
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
shaneyake avatar image
shaneyake answered ·

You should be able to add 1 generator to one of the Quattro's and if you disable switch as group, it will make L2 and L3 with the inverters.

2. No, unless it is perfectly synchronized 120degree out from the other inverter which is basically impossible.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Marc Schmaus avatar image Marc Schmaus commented ·

Thanks for your answer.

What do you mean with <switch as group>?