Hi,
I would like to replace one multiplus 48/10000 by two multiplus 48/5000 in parallel. Is there any disadvantage of this solution ?
Is it easy to make the master / slave control working ?
Thank you for your help !
Regards,
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Hi,
I would like to replace one multiplus 48/10000 by two multiplus 48/5000 in parallel. Is there any disadvantage of this solution ?
Is it easy to make the master / slave control working ?
Thank you for your help !
Regards,
Parallel configs take very careful wiring to make sure everything is symmetrical.
Attention to detail is everything as it is an advanced setup.
The configuration is the easy part.
Two systems are less efficient than one and the less accurate your installation is, the more imbalanced loads will be.
If you already have a 10k, short of certification requirements, there is no benefit to having 2 smaller inverters instead.
Make sure you do the training and read all the docs on these types of installations to avoid problems.
if once of both fail, the whole system is down
A possible reason to do this when when installing from new, but doesn't justify replacing a perfectly good 48/10000 with two 48/5000...
If one MP dies then as well as disconnecting the ve.bus I believe you have to physically disconnect from the battery and AC outputs, and probably also the AC input -- it would be helpful if someone from Victron could confirm exactly what is needed... ;-)
This could be done by removing fuses to the dead one if these are separate for the two MP (which IIRC they should be), if not then cables need disconnecting.
I guess this change can't be done from the Cerbo, it needs doing from a laptop or phone via the mk3?