270W solar panels- EasySolar 48/3000 (Multi) with MPPT 150/50- 4x200 Ah gel batteries in series for 48V . BMV 700 - CCGX Color control. No Grid feed in allowed . Grid available for AC IN.
I am having serious difficulties setting up ESS / Assistant with VEConfig.
When looking at what Virtual Switch can offer, I realize this is far enough for what I want to do.
1_ Use as much solar as possible to recharge the batteries ,
2- Set VS for Grid ACIn to come ON when batteries are too low (50 V) or when a heavy load is powered .
I have set up VS on VEConfig . All seem OK; I have "sent" the settings .
However, I do not see my Multi behaving according to the VS settings . Example . i have SET AC IN "ON" if more than 3000 W is requested , or if batteries get lower to 50 V.
Right now my batteries are 52 V, and my AC OUT loads are 500 w.
Until I solve the VS settings problem, I have my EasySolar "ACIN" breaker on "OFF" as I do not need , nor want any AC IN .
If I turn on the AC In breaker with these voltage / Watts described above, my AC In comes in ? It should not.
Did I forget something after setting VS on VEConfig ?
Thanks