Parallel Orion Tr Smart Chargers - Wire & Breaker Size?

What are the Wire & Breaker sizes for two Orion TR Smart 12/24-15A Chargers connected in parallel; see diagram below with questions. (The Single Charger at the top, is based on information provided in the Manual.) Note: CCP2 is a Customer Connection Point on the Ford Transit.

b2b-connections-041123.jpg

orion-tr smartorion dc-dc
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
kevgermany avatar image
kevgermany answered ·

Between starter and first busbar you have double the current of the single Orion example, so double the breaker sizes/wire guage (60A)

Between the busbars you are back to same wiring loads as the single installation, so as per manual.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

vanchitect avatar image vanchitect commented ·

After I posted the question...I was thinking that's what it would be. Thanks for the response.