Cerbo GX v2.89
MP 48/5000/70-100 v476
MPPT 250/100 VE.Can r2 v3.10
Pylontech batteries
DVCC forced on
SVS forced off
Pylontech is default battery monitor
Unable to charge above about 40% SoC
MPPT current starts throttling when MPPT reaches 52.4V while Pylontech/multimeter reports 49.6V. MPPT reports being under external control.
Why isn't MPPT being fed the Pylontech BMS voltage value?
This is not a new system. Uncertain of timing, but batteries were able to mostly charge to full pretty regularly, but not being able to attain more than 40% somewhat recently.
Originally there were four batteries. Two have generated faults and are being tested by the distributor. The remaining two do not indicate any faults.
Please note that this ~3V delta is present under charge AND discharge.
EDIT: I have enabled the MP battery monitor on the dashboard, and it reports within 0.1V of the Pylontech value.