question

chuff avatar image
chuff asked

Generator correction in firmware 502 on Quattro with gridcode selected

Pleas note that currently in the 502 firmware, the generator can be only selected on ACIN1 but not on ACIN2. Please add this fonction also on ACIN2 because on some ESS system with grid connected on ACIN1, the generator on ACIN2 is to be used in case of grid failure (backup fonction as presented in the ESS manual).

MultiPlus Quattro Inverter ChargerGeneratorfirmware update
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

djbower1 avatar image djbower1 commented ·

Agreed. I have always found it strange that there is conflicting information between their ess manual and training videos.


Could Victron please clarify which method is best practice????

0 Likes 0 ·
1 Answer
mvader (Victron Energy) avatar image
mvader (Victron Energy) answered ·

Hi both, yes I can clarify.

And in all honesty we changed our opinion/advice on that recently.

The advice for the generator is to be on AC in 1. Also for ESS systems.

More details on that are here:

https://professional.victronenergy.com/news/detail/178/

The in there mentioned last unsolved piece of the puzzle is making the genset start/stop in Venus OS also properly handle a generator connected to AC in 1. Which is whats currently being worked on and progressing nicely. Few more months max. Hopefully sooner.


1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

djbower1 avatar image djbower1 commented ·
Thanks for the info. Look forward to the update.