Hi all.
Yesterday I installed a new MPPT 70/10 to charge lead-acid a start battery from a lithium 48V bank (540Ah). I connected the start battery to the 12V battery terminals and checked the auto-detect in the VC app - all was fine. I then connected the load terminals to a 12V load buss and finally connected the 48V power to the PV terminals. All seemed fine and the start battery went through bulk-abs-float no problem.
This morning I got an Error 28 alarm on one of my other MPPTs - this one has 2x24V panels in series going into the PV terminals and the output goes to the same 48V buss that the new MPPT takes power from. PV on the old MPPT was over 80V - the other 3 MPPTs for my solar set up read from 55V to 67V as normal (72 cell panels). This should be easily handled by a 150/45 MPPT.
Seems odd that it was fine at installation (late in the day & not much solar input) and then caused an error when the sun got higher in the sky this morning. For completeness, there are actually two solar MPPTs in this circuit - the other one, connected to the same buss and set up the same way, seems fine with no errors and normal voltage, currently around 63V.
Any thoughts on what might be happening?
Also wondering whether the Load Output should be set to Always Off in this configuration since the intent is not to use it to help with normal loads - it's just being used as a charger. Is that what this setting does? And if so then is this the same as just not connecting it to the load buss?
Thanks in advance.