Looking at upgrading my RV solar to a 3 panel system on a new MPPT 100/20. Existing is 2*100W on an older controller. The older panels are discontinued so I am purchasing a 3rd panel that is not identical. Battery bank is dual 225Ah golf cart (in series = 12V)
New system would be:
2x Renogy 100W Panel modules
Voc 22.5V
Vmp 18.9V
Imp 5.29A
Isc 5.75A
1x Renogy 175W Panel module
Voc 21.6V
Vmp 18.1V
Imp 9.67A
Isc 10.31A
I've calculated these 3 panels can be run in parallel with only a 2.68% loss due to the difference in panel specifications. Panels will need to be individually fused due to the max fuse rating in the event of a short.
The updated array will output 365W at 17.95V @ 20.33A.
The Renogy calculator shows it's 129% oversized. Should be a good amount due to primary usage in the northern hemisphere, and they will be flat mounted.
My primary concern is: I've calculated the array short circuit (5.75A + 5.75A + 10.31A) = 21.81A. This number is tripping me up with regards to the 100/20 recommended max short circuit.
Does this prevent me from using the MPPT 100/20? Do I need to be looking at the MPPT 100/30?
Thanks.