Multi EVCS on one system - how will it handle excess solar?

Hi,
I have a cliente looking at 2 EVCS on one system connected to AC2 out of the MPII's but the following questions come to mind;

1) When both are configured to Auto to use excess solar, how will it handle this? Will it share the available excess power, prioritise one,...?
2) Will both chargers show up seperately in VRM?

3) Can I have one on auto to use surplus and the other programmed?

The setup will be ESS with the following as the main components;
3 x Multiplus II 48/5000 in parallel (15KVA 1 x 230V)
1 x RS MPPT 450/200
1 x MPPT 150/85
12 x Pylontech US3000C
1 x Cerbo GX
37 x Hyundai HiE-S440HG


Thanks in advacne

ev charging station
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Lucian Popescu (Victron Energy Staff) avatar image
Lucian Popescu (Victron Energy Staff) answered ·

Hi, we did some test and up to 50 charging stations on the same GX should be OK from the communication point of view.

Then, regarding power-sharing, at this moment, all the available power will be shared between them. We are planning to add priorities, but I can't say when.
On VRM, you can see them separately, if necessary, organized on AC IN or Ac Out, as you can see on the picture below.1679679297529.png

If you are a nerd (like me :) ), you can also create custom charging rules in Node-Red. We have nodes for charging stations, that allow configuring all the parameters.


1679679297529.png (77.5 KiB)