question

assyntdavid avatar image
assyntdavid asked

Have you installed the Victron EV charging station in the UK

Last week I installed the Victron EV charging station in the car port by our house (ie a garage without walls). Essentially it replaces an existing double 13A UK outlet. I decided on the Victron model because of its integration with the house ESS system, and first impressions are favourable so no regrets. (Not seriously tested yet).

Has anyone else installed the EV charging station in the UK with a similar set up? If so what additonal measures, if any, were taken with regard to a possible Protective Earthed Neutral fault on the supply. I contacted Victron directly for a comment/clarification on this point concerning UK regulations and received neither acknowledgement nor reply. Much is available on-line to read on this matter but there seems not to be a consensus as to when additional safety measures are needed and the correct (easiest) action to take. Can you help? If you have had the Victron charger installed in a car port what did your installer do?

Thanks in advance for any feedback.

Regards,

David

ev charging station
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

14 Answers
assyntdavid avatar image
assyntdavid answered ·

My clear conclusion following several contributions and much reading is that the Victron EV charging station does requires the installer to add both a type B RCD (not a type B RCBO) and a Matt:e PEN fault detection device. These can be purchased incorporated into one box but this will set you back an extra £300+.

This makes the Victron charger approx double the price of the Zappi charger. Integration into existing Victron systems is obviously way better with Victron's own charger but the Zappi seems to over much the same functionality. It is almost as if Victron is purposefully pricing itself out of the UK EV charger market which seems strange given the sales potential in coming years. What a shame.

Thanks to everyong who helped my researches.

Regards,

David

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Craig Chamberlain avatar image
Craig Chamberlain answered ·

Hi David,

I'm not an electrician but I am an electronics and electrical engineer and have also self-installed a similar EV charger (a Wallbox Pulsar Plus 7.4kW) and am very familiar with the regulations and PEN fault issue you mention. In fact I chose the Pulsar Plus because it was one of the few options at that time which included PEN fault detection along with the MyEnergi Zappi. I know there are others available today.

Firstly, you worried me a bit when describing the EV charger as replacing an existing 13A double socket. I'm hoping you only mean in terms of position and not the electrics, because the EV charge station needs at least a 6mm radial feed and will need a type A RCD and 40A MCB (or both combined in a 40A type A RCBO) to protect it. Depending on the age of your 13A socket wiring it might only have a type AC RCD which is not suitable to protect an EV charge socket because any DC components on the earth leakage might "block" the responsiveness of the RCD device. That could lead to it not performing correctly in the event of a fault which could be dangerous. This is all before we even talk about the PEN fault detection.

As for PEN faults, these are only an issue on TN-C-S (PME) earthing so presumably you already have determined that your earthing is of this type? If so then yes you do need PEN fault protection and this can either be integral to the EV charger (as it is with the Pulsar Plus and maybe(?) the Victron unit) or you can install a separate unit such as the Matt:e device. I had a read of the Victron data sheet for the EV charge and I can't tell for certain if it has PEN fault detection. It does talk about the following:

  • Detection for Relay Contact welded
  • Detection for missing protective conductor
  • Detection for missing Ground
  • Detection for shorted CP

So maybe the second one is PEN fault detection but it's not 100% clear. They might be describing this feature in generic terms rather than using more typical UK specific wording. With Wallbox, they describe it as "Integrated PEN fault protection" not just "detection". Wallbox also include a DC 6mA RCD integrated but also need a type A MCB+RCD/RCBO in addition.

I think you are right to press Victron to reveal the precise extent of protection provided and if in doubt consult an electrician who specialises in this area. Another option you can consider is to convert the EV charge station in to a TT earth but that is a whole other can of worms and you should probably get specialist advice to do that properly.

HTH, let me know if you have any other questions.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

daza avatar image
daza answered ·

There literature doesn't expressly say pen fault detection although they mention some standards and stick detection of missing ground in there, But they do say that it needs an RCD https://www.victronenergy.com/upload/documents/Datasheet-EV-Charging-Station-EN.pdf kinda need victron or distort to confirm this really as this is a key safety mech that all chargers need either in built or external via like a Matte device Looks like i was late to this party. @craigc is correct if its a 13Amp socket that you have replaced 2.5m cable is not suitable to handle a 40Amp load you would at least 6mm twin and earth clipped to a wall but your best off with SWA cable new connection to the fusebox purely for safety compared to the twin and earth. I'm only assuming its twin and earth based on the 13amp plug socket and only assuming its not a ring circuit.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Daniel avatar image
Daniel answered ·

Hi David,


If you already have a battery system installed working with your Victron charger this is ace!

You should already have an earth rod for your batteries in place so your EV charger will be earthed Via the rod and your distributors earthing arrangements which is in the new regulations now, to do both.

Next is you have to use a DP or switched natural as well and line (Live) 30ma TYPE A RCBO to supply your EV charger.

FuseBox 32A 6kA Double Pole Mini Compact RCBO - Type A - Curve C | ElectricalDirect

Also notify DNO soon as you can within 28 days

Single-Electric-Vehicle-Charge-Point-and-Heat-Pump-Installation-Application-Form.doc (live.com)

That’s all you need todo to meet the regs.


Hope this helps

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Craig Chamberlain avatar image Craig Chamberlain commented ·

I'm not so sure that you can share an earth rod between an EV charge point and rest of the house, especially if that earth rod is attached to the main earth terminal. That certainly wouldn't be considered a TT earth from the EV's perspective. As I understand it, the idea is to have the EV earth rod immediately adjacent to the EV charge point and completely isolated from the house earth. Normally you would run SWA cable which would be connected to the house earth but you would intentionally isolate the SWA armour at the EV charge point and label it as such. There are other concerns with earth rods such as distance from underground services etc.


I agree you need at least a type A RCD/RCBO but actually I notice in the Victron manual it says a type B but this is in reference to a 3 phase system so I'm not sure if type A is okay for single phase or not. Part of the BS7671 regs is to follow device manufacturer's instructions so you'd need to clarify this with Victron for single phase use. A type A should be okay though I think and is a lot cheaper than a type B.

Edit: I wonder if it needs a type B RCD because it doesn't have the 6mA DC RCD built in as the Wallbox Pulsar Plus has?


Re DNO notification, there were some changes introduced recently (Jan 1st I think) which tighten up on some requirements such as cyber security standards. But there is also a list of prerequisites that are needed in order to do a "notify after install" which might not apply. For example you need to know the DNO cut out fuse rating which might not be the same as the "100A" stated on the carrier. That rating is the maximum and you might have a 60A or 80A or 100A fuse fitted. I had to get the DNO to come out to confirm the fitted fuse in mine which did turn out to be 100A so was all good. You also need to calculate maximum demand and ensure it's within spec or you'll need to fit a device to regulate EV current in response to overall house demand. That might be part of the Victron EVCP design though so should be all good. These constraints are listed in section B of the doc you linked so the OP can have a read.

ps. I note that you are an electrician so feel free to ignore me! :))


Update: See this thread. Looks like it does NOT have PEN fault protection and DOES require a type B RCD. IIRC a type B RCD is around £200 and a Matt:e device is around £100 so you need to add £300 to the cost of the charger to compare with devices which have this built in. I'm a bit disappointed if this is true because I really liked the idea of integrating a Victron charger to my system at some point.

https://community.victronenergy.com/questions/139651/ev-charging-station-pen-protection-or-earth-rod.html">https://community.victronenergy.com/questions/139651/ev-charging-station-pen-protection-or-earth-rod.html

Note - you should probably ask @Betaoil what the source of this information was.

0 Likes 0 ·
assyntdavid avatar image
assyntdavid answered ·

Thank you @Craig Chamberlain et al. I did purposefully miss out wiring details, hoping for advice as to additonal PEN fault detection, etc. Given that the responses above indicate that doubt still remains regarding this, could @Guy Stewart (Victron Community Manager) possibly contribute and help here. The Victron charging station is not in the UK approved government list but that may well reflect its relative newness on the market. It seems to be an expensive but excellent piece of kit.

The feed to the previous 'double socket' is a dedicated armoured cable protected by a Wylex 30mA B curve type A RCBO put in place some time ago with this conversion in mind. (Every circuit in the house is protected by an RCBO. I was a strong convert to Earth Leakage Current devices, as they were called, over 40 years ago when they were installed in my then work environment, adjusted to 10mA leakage.)

The feed is 4mm2 as opposed to 6mm2, an economy I now regret. That said, is not a 4mm2 feed protected by a 32A RCBO OK for an (up to) 7kW device?

I am delaying contacting the DNO before clarifying these points. (The EV supply was switched off after install and remains off.) The house fuse is the usual 100A rating although the DNO at the time of install said they were going to fit a 60A fuse (another long story). In reality the batteries are charged overnight and during the day the house runs absolutely fine off grid from the 10000VA Mulitplus 2. Any EV charging would occur overnight. The batteries are also charged overnight (if there has been insufficent PV) but limited to around 1kW, so even then the max current drawn from the grid would be circa 40A.

Whilst my off grid battery set up is earthed by a series of interconnected earth rods arranged around the perimeter of the hut, the house ESS system is simply connected to the house earth, ie the incoming neutral/earth connector. Have I missed something here? Is an additional local earth required for house ESS? If so I have no idea how I achieve that. (A friend also has a house ESS (different manufacturer) recently installed in a new build. That definitely has no additional earth. In fact his house is in a rural location and the incoming supply meter and the only earth connection is located in a box at the boundary of his property approx 40m away from the house. All has been installed and approved by qualified electricians, but seemingly at odds to me with what you read about PEN faults.)

I would love to hear from Guy and also anyone who has had this charger installed and DNO notification by a fully qualified installer. Whilst not a qualified electrician (but I do have relevant qualifications) I have either fully wired, or extended, house wiring several times over the past forty or so years. They have always been tested and signed off by a suitably qualified person, but that route does seem to be getting progressively harder over time.

Thanks to all for your time and expertise, very much appreciated.

Regards,

David

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Craig Chamberlain avatar image Craig Chamberlain commented ·

Hi @assyntdavid thanks for clarifying your situation, that all makes sense.


Just to answer a couple of points - yes 4mm2 cable can carry up to 37A if clipped direct but regardless of that, it says in the EV charger manual in section 3 that "Recommended cable cross-section is 6mm2 / AWG 10." This is also where it says a Type B RCD is required (not to be confused with curve B). Note also that a 4mm2 cable will have significantly higher losses than a 6mm2 or 10mm2 cable and if the cable length is quite long then you might even be out of spec on voltage drop. For this reason I installed a 10mm2 cable for my own EV charger installation.

If you have a look at the flow chart HERE you'll see that you will almost certainly need to follow the "Apply to Connect" process and I expect you'll need your cut out fuse upgraded to at least 80A if not 100A. The DNO should be able to do this free of charge provided the service cable and other components are suitably rated.

Regarding your earthing arrangement - there is a regulation that states that you must not rely on the DNO earth if running in "island mode" which is where you have a grid failure and your inverter it running the house independently from battery. This is because in island mode you can't be sure that the DNO earth is still intact. Also, I understand it has become standard practice these days to install a local earth electrode on new installations anyway which helps to mitigate against PEN faults arising.

HTH

0 Likes 0 ·
daza avatar image
daza answered ·

@Craig Chamberlain yes you are correct that it has become standard practice for local earth the DNO doesn't want the responsibility for this anymore, that's why the new regs are talking about foundation earthing, now i wish i had the hindsight to throw a couple of rods in my extension foundation. Now I'm having to do a long run into the garden to get away from everything.

@assyntdavid

Right this is a mine field of a topic, So i done a dive into TNC-S with PME as that what mine is. And the issue is the neutral tired to earth bond that goes when the house is in island mode. The issue here is yes you can put an earth rod in the ground and make a TT system but its very hard to keep it a TT system looking at some of the requirements it has to be about 5meters plus from the incoming as to not feed connect to the grids earth again, next is that in the UK all under ground pipes should be bonded which means we've just done all that work and still got a TNC-S system also all metal pipes feed to neighbouring properties are also earthed which feeds back to you which keeps it a TNC-S system. PS it is essential that all metal pipes entering the property be bonded to earth for everyone in or outside that house coming into contact with metal pipes are safe.

Glad i replaced my last metal pipe with plastic so not tired to earth meaning i just need to keep away form the coming mains and any metal work. I see a lot of people are looking at the earth bonding relay but really don't see the point in this, yes the resistance is a lot lower on the DNO due to the PME but if the relay contacts get stuck you have a problem. I would rather sink 4 to 5 rods deep get a good earth obviously tested to make sure its within the 200ohms or better still 100ohms or lower.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

assyntdavid avatar image
assyntdavid answered ·

Thanks @Craig Chamberlain

I can easily change the RCBO to type B - I had missed that. The fuse is already 100A so fine there. I get that the PEN fault situation would be an issue in 'island mode'. Not at all sure how I install a local earth electrode given the house structure and the difficulties of caarying out the earth resistance tests. Something to sleep on!

David

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

l81ker avatar image
l81ker answered ·

According to Victron when I asked my dealer about this, it does have PEN fault detection. This is confirmed in the spec sheet https://www.victronenergy.com/upload/documents/Datasheet-EV-Charging-Station-EN.pdf which you can find on the product webpage.https://www.victronenergy.com/ev-charging/ev-charging-station

I didn't go for it yet as I'm awaiting the LAN connected version.


1679777871815.png


1679777871815.png (28.3 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

assyntdavid avatar image
assyntdavid answered ·

@l81ker I appreciate your response and would love to agree with you, but at the moment I am inclined to agree with the @Craig Chamberlain comment at the top that the documentation is ambiguous. The sceptic in me is also influenced by the fact that Victron has never added a simple comment to clarify this on the discussions on the forum even when invited directly by other and by me above to @Guy Stewart (Victron Community Manager). Neither did Victron reply when I emailed the question to them. Thus I feel I have to assume that it does not comply.

Forgive me asking, but do you have grounds for believing that your dealer has the technical expertise to reliably comment on this complex matter. There are several dealers/resellers out there who have minimal technical awareness of Victron equipment. For example, does your dealer also install and has thus registered these chargers with the local DNO? Did they, could they, forward a response from Victron to you?

I'd love to find out that the charger does comply with PEN fault detection, more because I want to continue to believe that Victron equipment is the best than the extra cost I need to fork out. And why is there not a type B RCD included in the device, then all the installer needs to do is fit the appropriate MCB in the consumer unit.

Hoping you can add clear ressurances re your dealer reply.

Regards,

David

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

l81ker avatar image l81ker commented ·
Hi David, I had to explain to my dealer what it meant and get them clear about it before they asked the Victron Rep. I think your approach is wise, given the lack of complete clarity coming forth officially.


0 Likes 0 ·
assyntdavid avatar image
assyntdavid answered ·

Thanks @l81ker for the update. Are you saying that having explained the issues to the dealer, the Vicron Rep indicate that the charger does satisfy the PEN fault requirements. I am still waiting for a local electrician to come round and do the necessary. I strongly suspect that by the time I have provided a local earth for the house (a good idea because of 'islanding') and also installed the Matt:e thingie it is going to be a case of 'belt and braces +++' but given the deafening silence from Victron that seems the best way forward. As an aside I detected a potential difference of 250mV between my newly installed house earth rods and the grid earth. It can be difficult to make sense of some the scare senarios posted on the electrical websites.

Regards,

David

2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

l81ker avatar image l81ker commented ·
yep. Very Simply Put: PME means two wires come to your house from the nearest transformer. "live" and "neutral", no actual 'earth'. These two wires arrive at your house and then an "earth" is split out from the neutral, and that "earth" is supposed to be bonded to any and everything in the house. If something goes wrong, any current that flows on that 'earth' path instead of the proper Neutral path is detected and trips the RCD.


Imagine the neutral line gets broken off at the grid transformer end... now the only return path is actual ground. No problem inside the house bc stuff just doesn't work - even tho everything is now floating at mains voltage - but outside you could have a car at mains voltage on the metalwork and your feet on the floor... that's why Hot Tubs, EV chargers etc all need a ground rod now.

Not for the earth return current, but to be sure the breakers trip. PEN fault detection "notices" the lost Protective Earth-Neutral and disconnects everything to protect the human.

Belt and Braces is a good approach because you have redundancy in the system, it costs more of course and means more ugly stuff on the wall.

Obviously this is a super simplified explanation, I just wrote this to help others grasp the concept more easily.

0 Likes 0 ·
l81ker avatar image l81ker l81ker commented ·

"Are you saying that having explained the issues to the dealer, the Vicron Rep indicate that the charger does satisfy the PEN fault requirements."

Yep, exactly that, but only on the phone. I haven't it in writing anywhere.

0 Likes 0 ·
semlohnhoj avatar image
semlohnhoj answered ·

I'm coming into this conversation a little late as I've just raised pretty much the same question again on this group. I guess I should have searched further.


My understanding is that if the charger doesn't have an RDC-DD device internally to detect DC leakage then you definitely need a Type B RCD under the latest regulations.


I just made the mistake of buying a new consumer unit from my local electrical distributor which is specifically labelled as an EV consumer unit which he told me had a Type B RCD. Turns out it's a Type A. The guy didn't really seem to understand the regs for EVs even though they sell them which makes me think lots of these are getting installed with incorrect protection. The DC issue can affect upstream RCDs as well so if you feed the EV charger from a consumer unit in a garage which is then fed from an MCB in your main consumer unit in the house and that has a Type AC or A RCD then that can be blinded to AC faults if there is DC leakage at the garage end that isn't protected properly. This would result in it not tripping due to leakage faults within your house which isn't good. This won't happen if the garage feed is directly to the DNO supply though.


I have an earth rod installed for my ESS system for when I'm islanding during the day as has been mentioned in this group. I also use it for my solar panels.


I wish there was some clarity about this EV charger. I have bought one and now it looks like I need a £300 consumer unit unless Victron can clarify. I'd rather know and pay the money for safety than be in the dark.


3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

semlohnhoj avatar image semlohnhoj commented ·

I noticed on the image below that the unit has a current sensor across all the phases (assuming you are using all three) which could be for picking up DC current but that's just me guessing:

screenshot-20230419-151529-youtube.jpg

It also has individual ones on each phase which I'd assume are for measuring the current on each phase.

0 Likes 0 ·
Craig Chamberlain avatar image Craig Chamberlain semlohnhoj commented ·

Here is a photo of the insides of my Wallbox Pulsar Plus. It's not particularly pretty to look at internally but is good quality, very compact and I would say highly refined. It also supports PEN fault detection, has 6mA DC RCD protection included and has a nicely designed mobile phone app that can support scheduling and various other features. And it was less than £600!

I would dearly love to be able to justify the Victron EV charger but it's currently priced way too high for what it is IMO.

screenshot-2023-04-20-at-010741.png

3 Likes 3 ·
semlohnhoj avatar image semlohnhoj Craig Chamberlain commented ·
Looks perfect. Like you say, is all built into the unit and appears compliant to the latest UK regulations for PEN and DC RCD. Shame we can't even establish if the Victron version is or not, seems bizarre.
0 Likes 0 ·
daza avatar image
daza answered ·

@Semlohnhoj i wouldn’t assume this could easily be a load balancing facility allowing you to connect more than one to the same supply cable, the only people that can clear this up is Victron.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

semlohnhoj avatar image
semlohnhoj answered ·

@Lucian Popescu (Victron Energy Staff) could you answer the question as to whether the EV Charger has internal DC RCD protection (RDC-DD) or do we need an external Type B RCD instead?

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.


Have you checked the datasheet and manual?


1681991963686.png


1681992097634.png





0 Likes 0 ·
1681991963686.png (127.8 KiB)
1681992097634.png (468.5 KiB)
semlohnhoj avatar image
semlohnhoj answered ·

Hi @Lucian Popescu (Victron Energy Staff) ,


Yes, I read the data sheet and manual but the information is specifically for 3 phase, not single phase. Can you confirm that a Type B is required for single phase as well?

Thanks,

John

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Yes, same for all, there is no RCD inside the current model. So if the local regulations are requiring RCD, you should add one.
1 Like 1 ·