Orion DC-DC, AGM, Lithium & Wakespeed

Hi all,

I am trying to understand the best way to charge both Lithium (House) and Led Acid (Start) incorporating a WakeSpeed regulator.

There are various diagrams online but it’s not totally clear how the combined setup works.

Would one of the two set ups below work? Or does anyone have a simple diagram to visualise the correct approach? Thanks.

victron-options.png


Lithium Batteryorion dc-dcAGM Batteryalternatorlynx bms
victron-options.png (123.7 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
jwfrary avatar image
jwfrary answered ·

Diagram 1 is what I intend to to in my setup. The load on the start bank is very modest so it's better to change that with a DC to DC charger.

Diagram 2 isn't a good idea with a large system, and would likely result in a short service life in the start battery and limited charging of the lithium bank (unless you double/triple up the dc to dc converters, but it's not really the best way.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

colm avatar image colm commented ·

(a) In Diagram 1, I assume I would need something like a battery isolator from the alternator also so as to charge the starter battery and the house lithium battery - and therefore not use the DC to DC?? - See Diagram 3. But, I understand that if I installed solar or another charging source for example then the starter battery would not benefit?? The other issue is I only can set up one charger profile. What's your view?

isolator.png

Diagram 3


(b) Another Option might be to install an ACR to isolate the battery when the Alternator is not running (assuming I don't need a isolated set up and everything has equal voltages)?

(c) Or, opt for Wiring diagram 2 - (note: the Alternator Shunt is incorrect as needs to be between all batteries) - but with additional DC to DC Chargers to increase the charging amps (Orion limited to 30)?

Any views on this would be greatly appreciated.


0 Likes 0 ·
isolator.png (185.5 KiB)
Robert avatar image
Robert answered ·

Hello, did you realise that when the BMS is not ATC, your Alternator doesn't charge?

For this reason it's not a good idea the controll your alternator by a BMS.

In worst case (with low temperature in your LFP Batterys) you run out energy because your starter battery wouldn't charge too.

Wich size of alternator, DC/DC Charger and Battery Bank we talk?

Best regards Robert


3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

colm avatar image colm commented ·

Hi Robert, the ATC set up is the recommended approach - see here. I am considering a 150Ah balmar and 600Ah Lithium house bank. We will also install solar.

0 Likes 0 ·
Show more comments

Related Resources

Additional resources still need to be added for this topic

Battery Compatibility

Did You Know - How to create a battery profile for non-Victron batteries?

Additional resources still need to be added for this topic

Victron DC to DC Converters Product Range

__________

LED indications, warnings, alarm and error codes

Lynx Smart BMS product page

Lynx Smart BMS online manual

Additional resources still need to be added for this topic