If two MPIIs 3kva 120s are already setup in 240/120 split phase can two more be added to the existing system to double the power, basically four MPIIs running split phase to a single critical load panel? Looking at future growth.
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
If two MPIIs 3kva 120s are already setup in 240/120 split phase can two more be added to the existing system to double the power, basically four MPIIs running split phase to a single critical load panel? Looking at future growth.
You will have less headcahes if you just bought bigger units and replaced the setup. You will also need to add more battery as well. And uograde cable size if you did not already start larger.
yes that would work, with above comment noted. inverters need to be the same madel and firmware version though. Care would be needed in setting up and correct wiring.
So 4 MPIIs can be setup in split phase. Do you happen to have any links on a setup like this? Acknowledge the guidance above on replacing and the wiring. Almost see this as a 2s2p setup and yes must be very careful with the ac-in and ac-out to make sure everything is aligned properly.
Important:
Use equal length and size battery conductors to the busbars. Do not oversize the cables as impedance here helps to balance the power between the inverters.
Use equal lengths of cable on the AC side for the same reason.
Sorry I don't have any links, but have run multi's in parallel before (single phase, not split) with no issues.