Orion 24/12 70

screenshot-20230314-101854-amazon-shopping.jpgHello.

I'm installing 6 Renogy 320 two strings 3, in parallel (8awg) to combiner box (8awg) to 150/70 mppt (2awg) to lynx using 4 12v Redodo 200ah plus Lifepo4 two string parallel 24v (4/0) to lynx powering a Sungoldpower 24v 4000w inverter charger (4/0) in a 2018 Coachman Freedom Liberty Express under the bed and the inverter is in pass-through with temperature actuated fans. AC lines from shore ran underneath to inverter then back to original WFCO destination.

My question among many. Can I install from lynx(24v) to the (2awg) Orion 24/12 70 to the existing 12v wires that lead to tounge battery ( instead of 12v battery use the 24/12 70) and not have to use a battery outside? And thus not having to change or alter STOCK converter WFCO.


This was the game plan and I'm all set to mount components to board and run wires.

victron community
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
kevgermany avatar image
kevgermany answered ·

Not sure about your proposed Orion, I don't think there's a 70A model.

In principle, what you propose is OK, as long as the cable to the house battery is adequate. Common ground is needed and it would help a lot to see your proposed wiring diagram.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

power-from-the-son avatar image
power-from-the-son answered ·

Thank you

Anyone else have any input? And yepper it's a 24/12 70