4ed9345a-231d-43c0-b580-e497b059060e.jpegI know each 3kva MPII (48v) needs a 50a breaker for grid input and load out (double poles for split phase). Can a MPII setup in split phase actually pass through 45-50a (11kw) when just using grid power, no assisting or charging?


Multiplus-II
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Paul B avatar image
Paul B answered ·

Yes that is correct

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

gutzpowers avatar image
gutzpowers answered ·

@Paul B thanks for the response. It’s incredible that small 3ka inverters like than can pass the full 50a through. Amazing, glad I’m looking at this for my home backup for split-phase. Obviously manually use less power when grid is down but awesome power passing through when grid is up.