Jonathan Manjoro asked

3 Phase Victron feeding back to grid

Hi there please assist.

I have a 3 x 3kVa Multiplus 2 inverters connected in 3 phase configuration, with 2 MPPTs and a Colour Control GX The limiting is being done by a Carlo Gavazzi EM24 meter, and it's connected properly, as per manual All equipment is on its latest firmware.

The system exports a significant amount of energy , average of 4 to 5 kilowatt hours per day.

On ESS setting on remote console, I have tried to change the Multiphase regulation between INDIVIDUAL PHASE and TOTAL OF ALL PHASES, but it's not making any difference

What could the problem be? and how can I solve it? Thank you

3 phase
6 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Alexandra avatar image Alexandra ♦ commented ·
@Jonathan Manjoro

And you dont have feedback from DC switched on? No other PV like an Ac pv inverter?

0 Likes 0 ·
Show more comments
Jons Collasius avatar image Jons Collasius commented ·

Have you loaded and configured the ESS assistant in VE Configure for the Multis?

0 Likes 0 ·
Show more comments
michaelvh avatar image michaelvh commented ·
Did you read the amount of kwh exported from your victron system or from your utility meter? Can be useful to compare these two.