I've got 8 x US5000, 4 long positive cables, and 4 long negative cables (same lengths in either scenario). The question is where to put those cables in the battery bank. The network cables will talk to the system and treat it as one big battery bank of 8 regardless, from what I understand, but I have some questions on differences in electricity flow between the two options.
My MPPTs can only charge at 400A, and I will set the inverter to not take more than 400A. So the cable ratings shouldn't be an issue.
The 2 banks of 4 is an option I've seen some do, also referred to as "double stacking." The questions I have on this option, what about the two batteries in the middle of each stack, will they get unbalanced since the current goes to the top and bottom batteries first? Also, does this drive a bigger circuit breaker/fuse for the cables because there are 4 batteries that can deliver short circuit current rather than the other option which would be limited to only 2 batteries providing current per set of cables? The manual says each battery has a short current/duration time of <2000A/1ms.
The Victron Wiring Unlimited Guide leads me to believe 4 banks of 2 might be better?
Because it suggests wiring batteries in parallel with one of these methods:
Thoughts?