Hi everyone my question is why is my inverter only putting 970 into the battery I just changed to the latest model and the old one charged way faster is there a setting that's incorrect somewhere?image1-1.jpeg

Multiplus-II
image1-1.jpeg (59.5 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Jason - UK avatar image
Jason - UK answered ·

@danracing Assuming you have the 24v Multiplus II 3kva, then as you reach the maximum voltage, the charger started to trottle back on the input to the batteries as to not overshoot the voltage.

4 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Jason - UK avatar image Jason - UK commented ·
@danracing What have you set the settings to in VE configure?
0 Likes 0 ·
danracing avatar image danracing Jason - UK commented ·
not sure done by tech guy

I'm trying to trouble shoot remotely

0 Likes 0 ·
danracing avatar image danracing commented ·
ok that seems right but the batteries are way down at 30 percent and its still in bulk literally at this speed 10 plus hrs away from being charged


0 Likes 0 ·
Jason - UK avatar image Jason - UK danracing commented ·
Ignore the 30% SoC for now until the battery has hit 100% voltage as the SoC is a estimate of the energy consumption form 100% so if you have not made it to 100% the SoC will be out of calibration. How long has the system been up and running?