Hi, in Australia we must install an Earth Fault Monitor in parallel to the MPPT250/100 resp. 250/85 if the Array voltage is above LV (120VDC).
We have installed an EFM Model DDEA from Thiim in Denmark. As soon as we turn on the Array DC circuit breaker the DDEA indicates an Earth Fault from MINUS to Earth. As soon as we disconnect the MPPT from the circuit the Earth Fault disappears. When we megger the resistance at the array from MINUS to Earth resp. PLUS to Earth the resistance is well above the minimum value of 30kOhm.
I contacted Thiim and there response was that there is an earth leakage in the MPPT from MINUS to Earth. That proves it as the Earth Fault disappears as soon as we disconnect the MPPT.
As we are going to have two more Off Grid system to install and have already purchased the Thiim ELM's i would appreciate your assistance solving this problem. Thank you.