3-phase Delta configuration Phoenix inverter 24/5000

Can we use Delta connection (without neutral, 400Volts phase-phase) in a 3 phase configuration of 3 pieces Phoenix 24/5000

Phoenix Inverter
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

tilo avatar image tilo commented ·

Do you mean if you can connect a consumer in Delta connection? What type of device or motor do you want to connect? Do you have a foto of the nameplate of the motor?

0 Likes 0 ·
1 Answer
mvader (Victron Energy) avatar image
mvader (Victron Energy) answered ·

Hi @Alexis Kalogerakis, no that is not possible. From the manual:


4.4.4 Three-phase operation

The Phoenix Inverter can also be used in 3-phase wye (Y) configuration. To this end, a connection between the devices is made by means of standard RJ45 UTP cables (the same as for parallel operation). The system (Inverters plus an optional control panel) will require subsequently configuration (see Section 5).

Pre-requisites: see Section 4.4.3.

Note: the Phoenix Inverter is not suitable for 3-phase delta (Δ) configuration.

3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

piet-roskam avatar image piet-roskam commented ·

Dag Matthijs, and in case of a 230V Delta network on board of a sailing yacht? Do we have any options?

0 Likes 0 ·
Johannes Boonstra (Victron Energy Staff) avatar image Johannes Boonstra (Victron Energy Staff) ♦♦ piet-roskam commented ·

Dag Piet, Yes we could do this with two units in serial connection and the 120deg splitphase settings. Then a third virtual phase is created which makes the system 3 x 230Vac. Or transformers inline creating 3p+n from 3p can be used.

1 Like 1 ·