question

eyub avatar image
eyub asked

stop battery charging from generator only

hello guys

I have a little bit complicated setting for a system with a quattro 10 kva and 2 ac input, the system is working in ESS mode. I would like to stop my batteries from being charged by the generator since it is a housing complex and the generator KWH is higher than the grid KWH cost so I don't want to charge the batteries with the generator but i need the generator for some essential load and i want to charge the batteries only using the grid is this posssible


battery chargingGenerator
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Alexandra avatar image
Alexandra answered ·

@eyub

Yes, you can disable the internal charger or reduce charge amps with the charge current control
assistant, based on ac input

2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

eyub avatar image eyub commented ·
I know that i can limit the charging current using dvcc but how can i do it based on ac input? is it from the color control or the ve configure ?
0 Likes 0 ·
Alexandra avatar image Alexandra ♦ eyub commented ·

Ve Configure. It is an assistant on the inverter.

0 Likes 0 ·