okelaa asked

Low and high limit (hysteresis) alarm

Hi there!

I have 48V system.

I am trying to understand why I am getting Low and High limit (hysteresis) alarm at 11:40am when the battery voltage is 51,94V? Is it normal or abnormal?

I am looking forward to a bit of advice, should I change system parameters or alarm rules or anything?

Here is the alarm message received yesterday 21st February 2023 11:40am:

img-9844.jpg


Below is the chart of the system parameters whole day 24h 21.Feb.2023

NB! Shunt - Current (A) means the battery charging current from the SmartSolar MPPT RS 450/100 - Tr

1677072922528.png

Current alarm rule:

1677073396841.png

I am very much looking for expert advice.

Kind regards,


alarm
img-9844.jpg (137.3 KiB)
1677072922528.png (751.4 KiB)
1677073396841.png (367.7 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
kevgermany avatar image
kevgermany answered ·

This is the recovery message. Maybe you can find the alarm message.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

kevgermany avatar image
kevgermany answered ·

Guessing that some time around 08:00 the voltage dropped too low, triggering the alarm. If you generate a graph covering less time, say from 07:00 to 09:00, you will get more information. With longer time periods on graphs, min max values tend to be averaged out.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

okelaa avatar image
okelaa answered ·

Yes, I am aware it was below 48V for some short duration but did not drop below 46V. Therefore I was wondering why the alarm is triggered when the lower limit 46V was not reached.


1677141794690.png


1677141794690.png (170.0 KiB)
3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

harold avatar image harold commented ·
may be a short dip, within the set interval update period of your system to VRM


1 Like 1 ·