did somebody install a Phoenix Smart Inverter with 24/5000 in the past and check the DC Connection Bolts?
I wanted to install a brand new Phoenix yesterday.
But it wasn't possible.
Both positive bolts got loose.
The torque was only 10Nm.
The negative bolts are super strong. 12Nm without problems.
Because only 90cm of length is used, Instead of 2x 95mm² wire, 2x 70mm² for positive and negative with M8 Terminals from Klauke.
Absolut no tension or spring force on the wire.
(i use super flexible wire from Titanex H01N2 D70)
After removing the Phoenix from the wall i wondering why the Busbar what´s goes inside is less than 2mm thick and the smallest cross-section is only 20x2mm
I hope my dealer can order a spare part.