Is this SOC correct?

Using the SmartShunt on dual 6v 230Ah batteries connected in series in my motorhome. Using VictronConnect to monitor the batteries. The batteries were only a couple weeks old and 100% charged when I installed the SS. We use the batteries to supply power for heating, lighting, electronics, etc. while boondocking. I have been monitoring the batteries while our motorhome is in storage. Today here's what VC reported. Does it make sense that VC is reporting my batteries have a SOC of 100% when the voltage is only 12.47?

screenshot-20230220-161401.jpgscreenshot-20230220-161342.jpg

SmartShuntVictronConnectSOC
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
kevgermany avatar image
kevgermany answered ·

The shunt can only measure current through it. It cannot account for self discharge within the batteries.SOC is based on current, not voltage. Shunt resets SOC to 100% to correct for drift, but only when batteries fully charged.

So the reading makes sense - in terms of how the shunt works. But is misleading.


It would be good to charge the batteries every month or so while it's in storage.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

JohnC avatar image
JohnC answered ·

Hi @SteveT

I agree with Kev, but your shunt settings probably could use some tuning too. Depends on your batt type, but we may be able to help if you ask.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

stevet avatar image
stevet answered ·

Should have mentioned the batteries are Napa lead acid deep cycle golf cart batteries. This is all new to me. I did a lot of reading on how to setup the VC app. Admittedly, I did not understand everything so I just kept most of the default settings. Suggestions are welcomed and appreciated. I will charge them up today. So I should just charge the batteries based on the reported voltage and not worry about SOC when the batteries are not being used?

4 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

JohnC avatar image JohnC ♦ commented ·

@SteveT

Are they these generic GC2's? https://www.napaonline.com/en/p/BAT8144?impressionRank=22

If so, I use clones of them, and these my shunt settings (for 48V)..

1677031751388.pngYou could raise Tail a little if you have short days or poor solar (so you mightn't reach it), say up to 1%. The 'true' Peukert of mine is 1.16, but I use 1.10 because it seems to work better at my lowish loads. The low 87% CEF is my summer setting (Pb's aren't efficient topping off a shallow discharge), but maybe 91% in winter. By all means tune them to suit yourself, but these will be better than the all-encompassing defaults.

I don't look at V much, Amps they can accept under charge is more important. These batts are quite reactive as Pbs go, and I find that 7A at Absorb V is 99.0% charged (and a good place to end Abs and drop to Float). In Float, that's my 0.6% (~1.3A), and then they're 100% SOC.

My charge settings (in your 12V lingo) are 14.4V Abs, 13.6V Float and -25mV/degC TempComp.

Mine are daily cyclers, not stored. But if they were, I'd give them a charge dose every coupla weeks. Electrolyte stratification and sulphation your enemies. They'll appreciate a little exercise, hey..

2 Likes 2 ·
1677031751388.png (32.1 KiB)
stevet avatar image stevet JohnC ♦ commented ·

Yes, the Napa 8144. Thanks for the suggestions. I will play around with the Tail and Peukert. Is your Charge Efficiency Factor at 87% because your batteries are older?

0 Likes 0 ·
Show more comments
nesswill avatar image nesswill commented ·

Completely agree with JohnC on this and as he says once you have "lived" with your system for a while you will get to know it and make small changes to optimise it for how you use it.

1 Like 1 ·