question

michael2019 avatar image
michael2019 asked

Controlling charge current with Quattro 15000 + BYD 13.8 pro Settings

I just installed a 15000 quattro + 2 parallel units of 13.8 BYD Box. I enabled battery monitor and I used 540AH Battery capacity. 108A as charging current (will the charging current be automatically determined by the BMS or the input battery charging current from the VE config plays a significant effect in the charging current?) float voltage is 55V, absorption voltage 55.2V. No assistant installed. No MPPT. No ESS settings.

VEConfigure 3gx deviceBYD
2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

michael2019 avatar image michael2019 commented ·

Battery low voltage data sent by the BMS is 43V, on the VE Config I set low battery shutdown to 44V. The picture of the BYD battery details and the video are attached.

0 Likes 0 ·
michael2019 avatar image michael2019 commented ·

Correction and further help are highly welcome

0 Likes 0 ·
1 Answer
Guy Stewart (Victron Community Manager) avatar image
Guy Stewart (Victron Community Manager) answered ·

Hi Michael,

Most of the information required for using this combination is here:

https://www.victronenergy.com/live/battery_compatibility:byd_b-box

Both the charge current limit set in the Quattro and the limit sent by the BMS will be used.

The lower limit will be the one that is applied.