LiFePo4 batteries not reaching full charge voltage, but are still fully charged

Hi all,


Grid parallel ESS

24V system

SmartShunt 500A

2x MPPT 100/30

Multiplus ii

Cerbo Gx

4x UltraMax LiFePo4 102Ah 24V "drop in" batteries with internal BMS in parallel in a busbar configuration (identical cable lengths)


I have 4x UltraMax LiFePo4 102Ah 24V "drop in" batteries with internal BMS (not connected/BMS compatible with Victron). These are in a parallel configuration for 408Ah. The system appears to be working well, with the batteries charging to 100% SoC according to the SmartShunt, and this 100% charge being reflected on all of the batteries internal BMS's (Bluetooth enabled) also. So the Victron SoC tallies up with the internal BMS SoC perfectly. This is good.


However, these batteries call for a 28.8V bulk/absorption charge voltage, yet they are reaching 100% charge according to their internal BMS's (and the SmartShunt) at a much lower voltage, around 27.6V. The MPPT's and MultiPlus ii are configured for bulk/absorption 28.8V and float 27.6V. I have noticed that the chargers are only ever in bulk mode, and never seen to transition to absorption or float, either by charging from the MultiPlus ii or the MPPT's.


Please find below attached screenshots of my MPPT's charger settings, MP ii settings and SmartShunt settings and also the specification sheets for the batteries.


MPPT charger settings page 1 of 2 Screenshot_2023-02-16-18-41-00-70_30b6efbd53acd6f273baafa7ca03da38.jpg

MPPT charger settings page 2 of 2 Screenshot_2023-02-16-18-41-05-60_30b6efbd53acd6f273baafa7ca03da38.jpg

SmartShunt settings Screenshot_2023-02-17-19-12-10-73_30b6efbd53acd6f273baafa7ca03da38.jpg

MultiPlus ii settings General tab MultiPlus ii General tab.png

MultiPlus ii settings Battery tab MultiPlus ii Charger tab.png

Battery specification sheet 1 of 2 Screenshot_2023-02-16-18-46-49-50_260528048de7f2f358f0056f785be619.jpg

Battery specification sheet 2 of 2 Screenshot_2023-02-16-18-46-55-72_260528048de7f2f358f0056f785be619.jpg

Battery manufacturer recommended charging parameters Screenshot_2023-02-16-18-47-17-72_260528048de7f2f358f0056f785be619.jpg


Please can someone help explain why this is happening, and if I should be concerned?


Many thanks.

battery chargingLithium Battery
10 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

klim8skeptic avatar image klim8skeptic ♦ commented ·

@Tom Ranson you forgot to post screenshots of your SmartShunt settings, and multi charge settings..

Victron has a really useful BMV Youtube tutorial. to help set up a BMV / SmartShunt.

I have noticed that the chargers are only ever in bulk mode, and never seen to transition to absorption or float, either by charging from the MultiPlus ii or the MPPT's.

The only time you can consider your Li batts fully charged is then they are held at the bulk / absorp voltage, and the charge current drops to 2 - 4% of the Ah capacity of your batt bank. That's 8 - 16a for your battery bank.

Your batt manufacturer has fairly wide range of charging voltages. 28 - 29.2v for bulk / absorp. And fairly miserly "absorp time settings. (this is where cell balancing occurs).

28.8v for bulk / absorp and 13.6v for float seems ok.

Aborp time really depends on how often the batteries get fully charged. Cells need balancing.

0 Likes 0 ·
Tom Ranson avatar image Tom Ranson klim8skeptic ♦ commented ·
@klim8skeptic many thanks for the advice.


So, even though my batteries open BMS's are showing 100%, they're not reaching the point of being able to cell balance properly? Why would a BMS tell me they're 100% when they're not actually? What's the harm to be done here by then not reaching balancing voltage?


I will respond with SmartShunt and MultiPlus screenshots later when home.

0 Likes 0 ·
Alexandra avatar image Alexandra ♦ Tom Ranson commented ·
Do the batteries stop taking in amps at the 27.6v? It is possible 100% SOC on both monitors are triggering early.

The datasheet shows to charge to 28.8v then have a of 0.02c or 2A per battery for balancing/absorp.

The chargers wont move out of bulk until you reach the target voltage which as you say you are not.

0 Likes 0 ·
Tom Ranson avatar image Tom Ranson Alexandra ♦ commented ·
@Alexandra I suspect that the 100% SoC is triggering earlier than it needs to, however should I not be able to rely on the internal BMS SoC calculation to a large extent?


No, they are still taking amps. I don't have a note of measurement for this as yet though. I will look at this in further detail when they are next on charge.


Is it that my charger settings are correct (I'm confident that there will be errors you'll spot, or areas to improve- and I look forward to hearing these from you), but the batteries need a longer charge cycle to reach 28.8V and then transition to absorb?

0 Likes 0 ·
Tom Ranson avatar image Tom Ranson Alexandra ♦ commented ·

@Alexandra I've editied the original post above to include the MP ii and SmartShunt settings screenshots also. I look forward to hearing your thoughts.

0 Likes 0 ·
Alexandra avatar image Alexandra ♦ Tom Ranson commented ·

@Tom Ranson

They definitely need to be left on charge until they reach the 28.8v. If they are not tripping and shutting down let the system sort it out.

I will spend some time looking at the settings and get back to you. But what i saw earlier before the update looked ok.


0 Likes 0 ·
Tom Ranson avatar image Tom Ranson Alexandra ♦ commented ·

@Alexandra You're a star, thank you so much. I look forward to hearing more.

1 Like 1 ·
Alexandra avatar image Alexandra ♦ Tom Ranson commented ·

@Tom Ranson

Yes , but also no on the internal bms. (And to some extent at least until we are sure the settings and sync are good also not the shunt)

I will check your updates when my brain is fresh. I know @klim8skeptic will also have some good further input here.

Leave the batteries on charge longer, they need to reach the target voltage. They are still taking in amps at 27.6v and not tripping so they should be fine to do so. Plus the datasheet says it can.

0 Likes 0 ·
Tom Ranson avatar image Tom Ranson Alexandra ♦ commented ·
@Alexandra Ok, noted. They will be going on for a 4 hour @ 50A (200 Ah approx) charge overnight (we have a dual rate electricity tarriff), and I'll see what the tail currrent looks like at the end of that charge cycle to see how much they are still drawing and what voltage they reach. I suspect it wont be anywhere near enough to push the voltage towards 28.8 though, as the highest I've seen to date is around 27.7V (and I also saw this after individually charging the batteries to BMS 100% SoC with their individual chargers, before I constructed the parallel bank).
0 Likes 0 ·
Tom Ranson avatar image Tom Ranson klim8skeptic ♦ commented ·
@klim8skeptic I've editied the original post above to include the MP ii and SmartShunt settings screenshots also. I look forward to hearing your thoughts.
0 Likes 0 ·
1 Answer
klim8skeptic avatar image
klim8skeptic answered ·

@Tom Ranson Your battery bank has not reached absorp voltage and is still taking current? It's not fully charged yet, give it more time on charge.


Have a look the the Volt / charge plot of your battery. Only at the very end of the charge cycle does the voltage rise rapidly. Once the absorp voltage has been reached, the current required the keep the voltage at this level plummets. At this stage your battery is probably at better than 98% Soc. A bit of time at the absorp voltage finishes topping the battery up, and gives the cell balancers time to work.

battery-soc.png

You didn't watch the bmv video? Set the charged voltage as 28.5v in the SmartShunt for now.

The battery monitor in the Multi is not good if you have DC charging sources. Un-tick "enable battery monitor". Put your effort into the SmartShunt for good Soc readings.

Did you fully charge the batteries before paralleling them?


battery-soc.png (269.7 KiB)
16 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Tom Ranson avatar image Tom Ranson commented ·

@klim8skeptic thank you, I see the graph and understand what you are saying about it.


So yes it appears as they are still taking full current at the end of an overnight charge cycle, they are not fully charged because they're not reaching approx 28.8V. Last night they reached approx 27.4, and the SmartShunt claimed 98% SoC. I wasn't able to check the individual BMS SoC's via Bluetooth as it was overnight, however given the behaviour I have already witnessed, I would hazard that they were also reading approx 98% SoC, as they appear to track quite accurately with the SmartShunt SoC.






screenshot-2023-02-18-10-14-23-45-bc2aea2f1887607a.jpg


I did watch the BMV video before writing this post, however I still found a few bits ambiguous, hence my settings probably aren't perfect. I will set the Shunt charged voltage to 28.5V as you suggest and disable the MP battery monitor. Yes I did individually charge the batteries before paralleling, until their internal BMS's read 100% SoC and all were at 27.7V resting (after several hours idle). However it seems they may not have been fully charged?

0 Likes 0 ·
Tom Ranson avatar image Tom Ranson commented ·

@klim8skeptic it's looking much better now. The MP ii has completed bulk and moved to absorption, sitting at 28.8V nicely and now with very low charging amps.

Is my Shunt tail current config correct at 4%?

Do I need tail current configured on the MPPTs?

Can you observe anything else I should adjust? Many thanks.

screenshot-2023-02-18-14-01-21-88-bc2aea2f1887607a.jpg

0 Likes 0 ·
klim8skeptic avatar image klim8skeptic ♦ Tom Ranson commented ·

The MP ii has completed bulk and moved to absorption, sitting at 28.8V nicely and now with very low charging amps.

Much better. Notice the voltage wriggling a bit at absorp voltage? I suspect that some of the batteries BMS's have disconnected their batt due to cells going overvolt. What does the BMS app show?

If that ^ is the case, the solution is to have the batts spend more time at the absorp voltage, that will give the BMS time to balance the offending cells.

Regarding time spent at absorp voltage. If your batts get fully charged a couple of times a week, absorp times can be shorter. If you only fully charge your batts a couple of times a month, absorp times should be longer.

Is my Shunt tail current config correct at 4%?

Leave it at 4% for now. The SmartShunt tail current is 1 of the values needed for the SmartShunt to auto sync the Soc to 100%. Not going to affect how the batts get charged.

Do I need tail current configured on the MPPTs?

More of a lead acid thing. Li need fixed time at aborp voltage.

Have you checked that your batts are equally sharing the charge / discharge currents? A semi decent clamp meter would be useful.