Hi all,
My first post, so be gentle. I have a victron smart shunt 500A (and temp sensor) with victron smartsolar mppt 100/30, 24V battery bank (2x FLA Banner 95751, C20 100Ah) and 2x 340W panels connected in parallel (shading on one of them). Both the shunt and mppt are in a bluetooth network and connected through ve.direct cable to raspberry pi for logging purposes.
I have had the system for ~6-7 months, and the shunt has had 19 automatic synchronisations with total Amps drawn -481.60Ah. The shunt shows total discharged energy: 11.92KWh and charged energy: 11.32KWh. So, somehow the batteries get undercharged by ~5% or 11.32/11.92 =~95%.
This does not seem normal to me. Should it not be the other way around, it shoud have put more in the batteries, accounting for the inneficiency of the FLA. The charge efficiency factor is 95% with Peukert 1.25. In all my thinking there should have been more charged than discharged to account for the 95% efficiency. It is like the brand new Banner FLA batteries are way more than 95% efficient in accepting charge or the shunt is undercounting. Nothing is bypassing the shunt in terms of energy, i.e. only one negative cable comes out of the battery and goes to the shunt, everything comes out of the other end. Maybe I need to calibrate the shunt's 0 again. I only have a non-victron inverter and no other power coming in other than the solar.
Every time I draw certain amount of Amps, then the mppt charges to ~95% of that. Consistent undercharging. I suspect that this is better than overcharging, but this will kill the batteries eventually.
Any help is more than appreciated!