smart shunt discharged energy 95% of charged energy

Hi all,

My first post, so be gentle. I have a victron smart shunt 500A (and temp sensor) with victron smartsolar mppt 100/30, 24V battery bank (2x FLA Banner 95751, C20 100Ah) and 2x 340W panels connected in parallel (shading on one of them). Both the shunt and mppt are in a bluetooth network and connected through ve.direct cable to raspberry pi for logging purposes.

I have had the system for ~6-7 months, and the shunt has had 19 automatic synchronisations with total Amps drawn -481.60Ah. The shunt shows total discharged energy: 11.92KWh and charged energy: 11.32KWh. So, somehow the batteries get undercharged by ~5% or 11.32/11.92 =~95%.

This does not seem normal to me. Should it not be the other way around, it shoud have put more in the batteries, accounting for the inneficiency of the FLA. The charge efficiency factor is 95% with Peukert 1.25. In all my thinking there should have been more charged than discharged to account for the 95% efficiency. It is like the brand new Banner FLA batteries are way more than 95% efficient in accepting charge or the shunt is undercounting. Nothing is bypassing the shunt in terms of energy, i.e. only one negative cable comes out of the battery and goes to the shunt, everything comes out of the other end. Maybe I need to calibrate the shunt's 0 again. I only have a non-victron inverter and no other power coming in other than the solar.

Every time I draw certain amount of Amps, then the mppt charges to ~95% of that. Consistent undercharging. I suspect that this is better than overcharging, but this will kill the batteries eventually.

Any help is more than appreciated!

screenshot-2023-02-13-at-161432.png

SmartShunt
4 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Alexandra avatar image Alexandra ♦ commented ·
@saskak

FLAs are not usually 95% efficiency. That more lithium territory.

Does the bank reach target voltage programmed? How long it is kept there? Do you have adaptive charge on?

1 Like 1 ·
Show more comments
1 Answer
saskak avatar image
saskak answered ·

I think I managed to solve it, but will have to monitor in the next few days to see. The Smartshunt was undercounting by ~0.08A, so either I have forgotten to zero it out at the beginning (zero calibrate) or it has drifted a bit with time. I simply removed the negative system cable from the shunt, so nothing coming out, reduced the current threshold to 0 in the victron connect app and saw -0.08 current coming out. Once I zero calibrated it, the current was 0.

So, in every 24h it was counting ~1.92Ah that have come out of the battery. So, my 0.10A current threshold was just above that and I never saw it, but it was accumulating with time. I will report back if that has fixed the issue, but I am nearly 100% that it will have fixed it.

Thank you all for the advice.


UPDATE:

Yes, that was the problem. The smartshunt was not zero calibrated or it has drifted with time. Probably I forgot to do it.

Last few days I was experimenting with small/large discharges and the difference between the discharged and charged energy is slowly reducing. Eventually will go to the normal ~85% for lead acid more charged than discharged.

Date Charge Discharged_Energy[KWh] ChargedEnergy[KWh] Difference[KWh]
15/02/2023 FullCharge[float at ~0.3A] 12.06 11.47 -0.59
16/02/2023 FullCharge[float at ~0.3A] 12.11 11.53 -0.58
17/02/2023 FullCharge[float at ~0.3A] 12.15 11.60 -0.55
19/02/2023 FullCharge[float at ~0.3A] 12.67 12.15 -0.52