Making 30A locking generator cable for AC IN of Multiplus II 48/8000?

My question:

What kind of cable should I use to connect the 30A output of my Honda 7000 generator to the AC IN of a Multiplus II 48/8000?

I have a 10 AWG cable with a 3 prong male end that connects to the generator. The cable is comprised of 3 individual wires wired into each prong of the male head (hot, ground, and neutral) and I still need to wire some fittings on them to connect to the MP2. But looking at the AC IN of the Multiplus I see two M6 lugs (L and N but no G). Where does the G wire go in the MP2?mp.png

cable.jpg

Multiplus-II
cable.jpg (260.6 KiB)
mp.png (3.4 MiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Alexandra avatar image
Alexandra answered ·


@AlaskanNoob

Does it not have the ground/earth bar?

It is also in the manual.

screenshot-20230213-164413.jpg


1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

alaskannoob avatar image alaskannoob commented ·
Thank you. I missed that in the manual and was going off a picture of my unit that isn't here with me, and didn't see the grounding bar. Many thanks!