question

Peter Buijs - NL avatar image
Peter Buijs - NL asked

EV Charging Station won't start charging Peugeot e-208

EVCS FW 1.24

The EVCS is grid connected, 3 phase, 16A. No gridmeter in between.

Everything seems to work fine.
- Webinterface > OK

- Venus on RasPi 2.93_03 > OK

- VictronConnect > OK

- VRM > OK

But it won't start charging our Peugeot E-208

EVCS Status says Low SoC

When we connect the E-208 to a public charging point it has 1hr 10min. to charge to complete...

ev charging station
3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Peter Buijs - NL avatar image Peter Buijs - NL commented ·

It appears that RTFM is still a valid recommendation ;-)

In the EVCS manual it says "when the GX device communication is not correctly configured the EVCS will have a status Low SoC".

I disabled the GX device in the EVCS webinterface and now it charges with 3P 11kW!

With VictronConnect it is easy to follow the status.


0 Likes 0 ·
Lucian Popescu (Victron Energy Staff) avatar image Lucian Popescu (Victron Energy Staff) ♦♦ Peter Buijs - NL commented ·
yes, because the EVCS can't read the SOC of the system
0 Likes 0 ·