Hi all,
I have wired up my inverter to supply the 240v breaker board from AC-Out 1 that has the boat sockets and the water boiler on, both on independent breakers.
The sockets all work fine but when I turn on the water heater on, which has a peak draw of 5000W (and am connected to the shore supply) it trips the marina shore supply (and the breakers in the boat).
My question is two part:
1. I assumed that when on shore power that the 3000w limit would not apply?
2. If I connect the water heater to AC-Out 2 (only avalable when shore power is connected) then will 5000w output still be accepted by the mutliplus and pass through the power or does the load still need to be below 3000W?
P.S The water boiler was working fine when the shore supply went direct to it before I installed the inverter (two days ago) so the power demand is fine for the shore supply.
Thanks in advance!
Dudley