Can someone expert advise me how many EasySolar-II (48/5000/70-50 MPPT 250/100 GX) can be used in parallel for a single phase system? How much can be the maximum system size in a single phase using them?
Thank you
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Hi,
Can someone expert advise me how many EasySolar-II (48/5000/70-50 MPPT 250/100 GX) can be used in parallel for a single phase system? How much can be the maximum system size in a single phase using them?
Thank you
You can have up to 6 MultiPlus-II units connected in parallel.
EasySolar-II has MultiPlus-II unit inside but also MPPT and GX.
You cannot have more than 1 GX in the system therefore you will have to physically disconnect additional GX units and leave only one.
The better (cheaper) way is to have one ES-II unit in the system and add MP-II units (same power) in parallel to it.
Even better way is to have MP-II units connected in parallel and use externally one GX unit and as many MPPT units as you need.