1.
The cable entry is not big enough to feed the cable into the multiplus2.
Any ideas on how to fix this in a safe and acceptable manner?
2.
Is it safe to insert the finestranded boat cable into the spring loaded terminal?
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
1.
The cable entry is not big enough to feed the cable into the multiplus2.
Any ideas on how to fix this in a safe and acceptable manner?
2.
Is it safe to insert the finestranded boat cable into the spring loaded terminal?
To insert fine stranded wire first give a little twist to the bare wire and ensure that there are no stray strands. Insert a small screwdriver into the connector release socket to open the spring loaded connector, insert the wire, then remove the screwdriver.
Have a look at this thread on the same subject:
https://community.victronenergy.com/questions/171883/ac-cable-sizing-for-multiplus-ii-485000230.html
Thank you,
But look at those answers.
VICTRON, help us out please.
Are these units even suitable for installation onboard boats/yachts?
The cable entry is not big enough to feed the cable into the multiplus2.
Are you having trouble feeding the cable through the grommet?
Is it safe to insert the finestranded boat cable into the spring loaded terminal?
The manual mentions to use a ferrule.
Are these units even suitable for installation onboard boats/yachts?
Dont forget the galvanic isolation.