@Guy Stewart (Victron Community Manager) I have seen several topics or questions on the same issue with no solutions regarding power assist. I have 2 multiplus2 2x120 24/3000 in parallel in an RV. Input current limit set @ 18.6 (the lowest it can go with power assist on) with loads @18.2 the inverters are only pulling 10amp from shore with the rest being pulled from batteries. I let it go for several minutes in hopes that it would level out somewhere closer to the input current limit but it stays at 10amp. Obviously this is not optimal as it will just continue to drain the battery bank. I would expect to see maybe a few amps difference between the input limit setting and the current drawn for a safety margin but this seems very excessive, about 46% if my math is close. This seems to be an issue that has been brought up repeatedly with no real answer or solution. Is victron working on this?
Both inverters are running 498 firmware, imbalance on the ac side is within about 15 watts and DC side within 2 amps. Power assist and dynamic current limiter are ticked, weak ac input is not.