ESS Fronius PV setup on AC input Victron training

Hi I followed the training video but looking at the ESS PV inverters I do have a Fronius inverter on the AC input so selected no but the training seems to imply that you select yes regardless whether its on the AC input or output, can any one clarify what the setting should be?


1675168819405.png

ESS
1675168819405.png (184.2 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

6 Answers
Rob Duthie avatar image
Rob Duthie answered ·

Hi

That is correct.

Regards

Rob D

NZ

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Craig Robinson avatar image
Craig Robinson answered ·

Thanks Rod so do you select yes even if the PV inverter is on the AC input of the inverter

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Rob Duthie avatar image Rob Duthie commented ·
Hi

You select no!!! read the panel as it explains what is required to do next in answering the questions of what you are trying to setup etc.

0 Likes 0 ·
Craig Robinson avatar image
Craig Robinson answered ·

OK Rod that's what I thought thanks

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Craig Robinson avatar image
Craig Robinson answered ·

Simple setup FRONIUS on AC input side, Pylontech 3000c x3 with BMS into Cerbo, Victron Energy meter, and multi II 5000 with firmware 501 ESS optimised with battery life (Active SOC limit 70% seems very high for these batteries but as the have only been connected for 5 days with very little load only simulation loads on the AC out and AC in to check grid feed in which does not seems to work very fast eg if I turn on the AC in load it does try to zero out but when removed feeds back into the grid even max feeding is set to zero, Any one got any ideas


1675326745953.png


1675329817674.png


1675326745953.png (59.9 KiB)
1675329817674.png (56.2 KiB)
ess-ac-input.mp4 (21.9 MiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Rob Duthie avatar image
Rob Duthie answered ·

Just follow as said, waht are yuor ess settings?

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Craig Robinson avatar image
Craig Robinson answered ·

ESS settings as shown in the images from the ESS manual I assume the Fronius is on the output of the inverter as I don't get the same settings as shown below can anyone confirm and if so what are the settings if on the AC input side of the inverter