Hi Victron team,
Hi community,
I operate three MultiPlus II 48V 3000/35-35. One per phase with activated ESS in Germany.
I have the problem that per Multi on one phase never more than 1600 to 1800 watts are delivered.
According to the data sheet, this is the power to which the Multi is adjusted when the temperature exceeds 65 degrees.
I can't not explain the power limit. The ambient temperature is just under 20 degrees and I don't think that the electronics in quasi standby already reaches 65 degrees.
The behaviour is generally given even if the multis did not have to deliver a higher power output for several hours before and the battery has long been charged.
Is it possible to determine the cause of the limitation?
Parameters that are transferred to the VRM or can be called up via MQTT / D-BUS / Modbus? I have not found a way to query the temperatures of the individual multis directly.
The battery (a BYD B-Box) is not the cause according to CCGX.
In the case of simultaneous power consumption over different phases/multis, the battery is discharged and does not limit the power.
The battery parameter of the B-BOX for maximum discharge power is 105A.
The maximum output 1600 - 1800 watts per Multi correspond to 32A depending on the battery voltage (between 51V and 52V), which corresponds to the power limitation on the AC side.
Load on 2 phases:
Alarm Status Multis:
Battery parameter B-Box:
Alarm Status Multis:
Multis status:
During the test of a mains disconnection and the behaviour of the multis (main switch to mains OFF and change-over switch to AC OUT of the multis) I noticed that the multis deliver more than 1800 watts. Without mains and without ESS I had the impression that the limitation didn't work.
Thank you.
Greetings from the black forest,
Martin