3phase Mp2 48/5000/30 with Pylontech 5000 - ESS trouble

Hi,

I use 3x MP2 48/5000/70 in a three phase system with 2x Pylontech U5000. It is all installed fix at home, no mobile solution. As long as I do not try to configure a ES, it is working like a charm. It changes the batteries and discharges them in case of switching off AC input.

Even configuring an ESS seems to work from VEConfigure for each single of the MP2. But then in the Remote-Console there are no ESS-Assistants available, strange enough.

1675014834873.png

The battery itself is communicating to the Cerbo, and I got the impression that this is doing a kind "whipping out" my ESS settings again, like overwriting my settings done in VEConfigure. Not sure, but it looks like.

1675014951744.png


All my firmware is upgraded to the latest version:

1675015130336.png


Does anyone please have an idea where the problem with the ESS might be coming from?

As I am still waiting to the delivery of my energy meter (EM24), is it possible that this is a prerequisite? If so, why this ist not mentioned by the software? And if not - how to fix my problem, please?

kind regards


ESS
1675014834873.png (18.5 KiB)
1675014951744.png (30.2 KiB)
1675015130336.png (52.9 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

5 Answers
marekp avatar image
marekp answered ·

@Fonsel

I understand that you used VEconfigure to configure the ESS Assistant, but did you upload this ESS Assistant into MP-II after configuring it?

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

fonsel avatar image fonsel commented ·

shure, and I could even download this configuration from the MP2 again. After some time, the configuration "disappeared" from the MP2.

So I got two theories:

- either the Cerbo gets "overwritten" by the Pylontechs

- or the Cerbo make a kind of a cleanup as it might not accept ESS without an energy meter.

I am quite sure there are other, more reasonable explanations out there?

0 Likes 0 ·
fonsel avatar image
fonsel answered ·

As soon as I installed the EM24 I could configure the ESS without any problem.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Alexandra avatar image
Alexandra answered ·

@Fonsel

I have all my ESS syemstems running without a grid meter. It is not a requirement for Victrons side to work.

Did you install the assistant on all the inverters? Usually the ess no assistant fpund message, is because there is no assistant on the devices.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Glen avatar image
Glen answered ·

seems no ESS Assistent is installed .


Do this :

1680800663517.png


then on ALL 3 MP2 install ESS Assistent :

1680800720222.png



repeat this with L2 and L3

and of course Save :-)


did you update the MK3 while you update Firmware to 501 ?

older ESS Release did not work with new Firmware


got 3Phase ESS MP2-5000 with Pylons working :

1680801366157.png


1680800663517.png (83.2 KiB)
1680800720222.png (36.1 KiB)
1680801366157.png (39.5 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

fonsel avatar image
fonsel answered ·

Thanks a lot. Maybe I did a firmware update in between which might have erased my assistants.

2 |3000