Upgrading - swap MPPT 150/100 to 250/100 or get 2 additional 100/20 ?

Dear community,

I want to add four 590W panels to the roof. Before there were already 12 of them, 3s4p. Would you advice that I swap my MPPT150/100 for an MPPT250/100, to create a 4s4p, or instead get 2 additional MPPT100/20 with 2s1p each? All panels have the same orientation, but the shadow situation is complicated.

Pro buying two small MPPTs (instead of a Smart Solar MPPT250/100)
+ Having more MPPTs could be a benefit when there are difficult shadows
+ I understand that the maximum output of MPPT150/100 and MPPT250/100 are actually the same (5800W at 48V), so having three MPPTs would increase the theoretical maximum peak
+ Probably cheaper than selling the used MPPT150/100 and getting a new one

Against buying two small MPPTs (and for getting a MPPT250/100)
- adding one of the panel to each paralleled string would also help with the shadows, no big advantage of extra MPPTs
- having separate MPPTs means longer cables at lower voltages (2 more strings with 2 panels with Impp=17,25A open Voc=41,2V each) - thus, higher loss
- MPPTs might switch on a bit later, when only two panels in series

Any recommendations?
Thank you


MPPT ControllersMPPT SmartSolar
7 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

seb71 avatar image seb71 commented ·

Are the additional PV panels exactlly the same make and model as the old ones?

You wrote about shadow issues, but without details. Assuming the string voltage would be safe (should be if the new panels are the same as the old panels and they are presumably safe for your existing 150/100), why not get just another Smart Solar 150/xx with 3s1p or 3s2p (if you have space and money for 6 panels)?

100/xx models are to limiting for future upgrades.

Do you have a GX device in that system?

1 Like 1 ·