Can I use Multiplus(first version) 12/3000/120-50 with 200Ah Lifepo4 battery

So I bought components for a camper year ago, but because of multiple reasons get to installing components only now. And in manual for Multiplus(first version) I discovered that minimum recommended capacity is 400Ah.

screenshot-2023-01-23-at-170816.png

Initially the plan was to buy two such batteries but now this is not an option.

1. So is it possible to use it with such battery, or it will damage it or wouldn't be function properly? I think currently loads should be not more then 1000 watts

2. Should I set up inverter settings so it wouldn't be allowing to discharge battery more then recommended amount of Amps(not really sure if such thing exist).

inverter current draw
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
kevgermany avatar image
kevgermany answered ·

One thousand W is about 80A at 12V. Ok for short periods, but the battery won't last long if you over do it.

Charge current can be limited by limiting input current to some extent, or if you have a GX device in the system, enable DVCC and that has a charge current limit setting.

2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

kostya avatar image kostya commented ·

Yep, I have Cerbo GX. Thank you.

So if I understand right the point of recommended capacity 400-1200Ah because if I use inverter at around 60-90% of load it wouldn't drain battery too fast which could lead to battery damage?

And so as I understand 70mm wire with 200A fuse should be more then enough for my situation(for battery and from bas to multiplus)?

0 Likes 0 ·
Show more comments