question

purei avatar image
purei asked

Multiplus-II stops charging when 51V are reached

Hi everybody,

My problematic :

I've got an off grid installation. And, specially at winter, i need to charge my batteries with a generator. But, after all updates of my installation components, the converter switch to inverter only when the SOC (State Of Charge) reached 51V. Does anybody knows why ?

My installation :

Multiplus-II 48V/5000kva firmware 500

CerboGX V2.92

Lynx Busbar

MPPT SmartSolar 150/70 rev2 V3.13

4 Pylontech Batteries US2000C, V2.22 (With batteryView software)

My settings :

I followed pylontech recommendations for MP2 settings from here : https://www.victronenergy.com/live/battery_compatibility:pylontech_phantom

multiplus-chargertab.pngCharger tab

The cerboGX is correctly wired and configured. It have all the informations from the MPPT, the batteries and the multiplus.

Symptoms :

When the SOC is near 20/30% ans no sun to the horizon, i start the generator. MP2 switch to charger mode and the charging starts in bulk mode. Batteries voltage is near 49V at this moment. The charging is effective until the voltage reach 50V and MP2 switch to absorbtion. Charging continues and when the voltage reach near of 51V, MP2 switch to inverter mode and the charging stops. I can replug the generator, MP2 switch to bulk, then absorbtion, then inverter mode.

What i tried :

I tried to setup the AC IN conditional with :
- ACIN ON if SOC < 100%
- ACIN OFF if voltage reach 64V (It's a volunteer high value for testing)

I tried to use WEAK AC, UPS function, Dynamic Current limit, PowerAssist

I tried to reset the Cerbo and setting it from scratch

I tried to reset the MP2 and setting it from scratch

I tried to warm up batteries to 15°C/20°C to be sure that's not the problem.

The generator is perfectly functionnal

What i need :

Some new ideas :)

Does anybody knows if i can find the FULL logs of the MP2 ? Maybe i could find something in it. I don't know what for now but i can look deeper into it.

Multiplus-IIbattery chargingPylontechGeneratorSOC
11 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

snoobler avatar image snoobler commented ·

DVCC settings?

0 Likes 0 ·
purei avatar image purei snoobler commented ·

DVCC settingsdvcc-settings.png

0 Likes 0 ·
dvcc-settings.png (29.8 KiB)
seb71 avatar image seb71 commented ·

The charging is effective until the voltage reach 50V and MP2 switch to absorbtion.

Is this correct?

Because according to your settings, the switch from Bulk to Absorption should be when the battery voltage reaches 52V.


Are you using any Assistants in Multiplus?

0 Likes 0 ·
purei avatar image purei seb71 commented ·

Because according to your settings, the switch from Bulk to Absorption should be when the battery voltage reaches 52V.

That's exactly what i thought at the beginning. But in fact, it not seems to works like that. How could i confirm the correct functionality ?

No assistant because virtual switch is in use

no-assistant.png


0 Likes 0 ·
no-assistant.png (21.5 KiB)
Show more comments
purei avatar image purei commented ·

I tried again some settings modifications. Battery monitor from general tab, WeakAC from grid Tab and dynamic current limiter with no succes.

But i download all theses tests in a CVS file if someone wants to find something relevant. (it's a .log file but can be opened with .XLS or .CSV reader) Generator_disconection.log

Just one last question, does anybody know if i can ask help from an official Victron expert by any way ? Phone, mail or other.


0 Likes 0 ·