The setup is 3x Multiplus II 48/5000/70-50 in parallel mode single phase.
One Multiplus is from 2020. The other two are new from 2022.
AC cable lengths are equal and not oversized.
DC cable impedances are equal as possible between the units.
Unfortunately, the Muptiplus from 2020 draws a much higher current from the battery than the two new ones. The two new Multiplus currents are almost equal.
Test Inverting | Test Charging | |||||||
Nr. | Serial number | AC length [m] | AC [mm²] | DC [mm²] | Firmware | AC Limit [A] | DC [A] | DC [A] |
1 | HQ2219MY2DF | 6 | 6 | 70 | 497 | 10 | 37 | 16 |
2 | HQ2218AXMNP | 6 | 6 | 70 | 497 | 10 | 38 | 18 |
3 | HQ2037MH5DX | 6 | 6 | 70 | 497 | 10 | 47 | 39 |
It seems that the "problem" is the old Multiplus from 2020. I think there were design changes on the PCB. PCB dimensions have changed. And the new ones show an unpopulated terminal block. (see pictures)
I bought the old and new MP at different shops.
I am not sure who can give support.
Can someone from Victron check (Serial numbers) if the Multiplus can work together?