Victron EV charger does not work off-grid?

After testing and reading through Victron documentation, it appears the Victron EV charger does not function as an off-grid EV charger. This is a little disappointing as one would assume the charger could function in auto mode, as indicated in the product description, to prevent the battery from being discharged below a certain SOC, when used off-grid. It appears the auto function is only operational when the system is used in AC-coupled ESS configuration (grid-connected).

System specs:

- Multiplus2 5KVA, 7.4kW DC-coupled solar, 16kWh self-managed LFP

- Victron EV charger - Firmware version 1.23

- CCGX

Unless I have somehow configured it incorrectly, it appears a regular EV charger could do a similar job. I have read that Victron is working on an improved algorithm, and I'm assuming this would address the lack of off-grid functionality.

As indicated in the attached photo, the EV charger will not function in auto mode even when the batteries are full, and there is ample generation. It just indicates "waiting sun"

20230120-133530-hdr.jpg


ev charging station
4 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Hi, it is explained in the manual that automatic mode is only for grid connected systems. But you can still use manual mode and define minimum SOC to stop charging. And yes, a new algorithm will be added, functional for offgrid systems.

1 Like 1 ·
Show more comments
1 Answer
Lucian Popescu (Victron Energy Staff) avatar image
Lucian Popescu (Victron Energy Staff) answered ·

You can do that automatically over node-red, not sure if you are into this. Even based on weather prognosis for the next days.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.