Hi, We have two 75/15 Blue Solar charge controllers, each connected to a rigid 175w panel on our pilothouse roof. Both are installed the same way - power from the panel feeds to a 20 amp breaker and then to the controller. From the controller the feed goes to a 25 amp fuse and then to the battery bus to feed the house bank.
Both have worked flawlessly since July, but last week the port controller stopped working. I am getting 26-30 volts coming from each panel at the panel outlet wires, and the same reading at the panel side of the breaker. For the one that is causing trouble, I get 25-30 volts when the breaker is off. If I turn on the breaker, the voltage at the breaker and as read at the charge controller is 12.56 - about .2 volts less than what the battery voltage is showing. The controller state is "off" and no watts are showing.
I have checked all wiring connections, replaced the breaker, replaced the MC4 connectors to the panel wiring and checked the fuse in the controller and between the controller and battery. I'm at a bit of a loss at this point. The other panel is wired exactly the same, and continues to work well.
I can provide the vcsf file for the controller in question.
Thanks in advance for any suggestions! - Tom