question

rrofes avatar image
rrofes asked

Adjust scheduled charging current?

Hi,


Is there a way to set the charge rate (drawn from grid) in ESS scheduled charging?

When I activate scheduled charging the system starts to charge batteries at its maximum current capability and this exceeds the power of my contract, so the company meter opens the circuit because of maximum power exceeded.

I have two multipluses 5000 48 working in parallel and 21.6kWh batteries.

Thanks community!

battery charging
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Alexandra avatar image
Alexandra answered ·

@rrofes

Reduce the input current limit to be under the incoming limit.

4 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Alexandra avatar image Alexandra ♦ commented ·
Remeber to make it half as you have a parallel system, so two units draw that power.
0 Likes 0 ·